#184917 - 02/25/09 07:03 PM flexible cord thru drop ceiling?  
CRW  Offline
Member
Joined: Feb 2001
Posts: 159
Bethlehem, PA USA
Are there any scenarios where you can run a flexible cord through a drop ceiling? I was told we could run a cord from a box above a ceiling, through the tile, with a cord connector on the end. This is for an appliance that is in the middle of an institutional kitchen, away from the wall, so we can't use a fixed receptacle. 400.8(2) seems to not permit this, but it also says, "Unless specifically permitted in 400.7..." which could then refer to 400.7(6)&(8). I questioned this whole thing at work (without citing the actual code, I didn't have it with me at the time) but the foreman said it was OK to do. What do you think?


Work Gear for Electricians and the Trades

#184919 - 02/25/09 07:29 PM Re: flexible cord thru drop ceiling? [Re: CRW]  
leland  Offline
Member
Joined: Aug 2007
Posts: 853
Lowell area, Ma. USA
400.7 says nothing of passing through ceilings. it speaks to cords for equipment.
400.8 is the guide.

I would install a ceiling box and drop a cord with strain relief and twist lock cap.Don't forget,if it is 120 volt 15 or 20A GFCI is needed. 210.8(B)(2)

Last edited by leland; 02/25/09 07:30 PM. Reason: 210.8

#184921 - 02/25/09 08:56 PM Re: flexible cord thru drop ceiling? [Re: leland]  
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
Passing a cord through the ceiling tile, as you describe, is a code violation in two ways: there's a flexible cord above the grid, and the cord is passing through a partition.

That said ... I recognize that this is often done, and that circumstances often make even a ceiling box impractical. I'm not quite sure where to go with this ... maybe a proposal for the next NEC cycle - but I'm not sure how one would write it.

Drop ceilings, once the 'wunderkind' of building, are quickly becoming a major headache. Perhaps their time has passed.


#184927 - 02/25/09 09:49 PM Re: flexible cord thru drop ceiling? [Re: renosteinke]  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,803
Brick, NJ USA
Another old addage from NJ....

"Drop ceilings hide a multitude of sins"

That said, cord thru the tile is a no-no. A ceiling grid mounted box, suitable coverm strain relief, & TL is accepted

However, a TL recept mounted in the ceiling box, face down, that the cord from the equip plugs into may be a better way.

Some AHJ's cite the cord from the ceiling box in the first scenario as using cord for permanent wiring, and red flag this, absed on 400.7 & 400.8 interpertations.


John


Member Spotlight
Attic Rat
Attic Rat
Bergen Co.,N.J. USA
Posts: 524
Joined: December 2003
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.014s Queries: 15 (0.003s) Memory: 0.7593 MB (Peak: 0.8899 MB) Zlib enabled. Server Time: 2017-03-28 04:12:50 UTC