The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Locked rotor, no burnout
by andey
Today at 04:48 AM
Temporarily feeding a panel...
by Potseal
Yesterday at 11:05 PM
Massive power outage South Australia
by Meadow
Yesterday at 06:46 AM
short circuit??
by Meadow
Yesterday at 06:43 AM
Norwegian power?
by Meadow
Yesterday at 06:36 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 14
sparky 10
sparky66wv 8
gfretwell 8
Potseal 7
Who's Online
0 registered (), 268 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 3 1 2 3 >
Topic Options
Rate This Topic
#184845 - 02/23/09 05:13 PM 208 volt contactor
rcksmith127 Offline
Member

Registered: 04/15/05
Posts: 33
Loc: Danvers, Ma, USA
Need some help. Are there voltage ranges for a coil? I have a 3 phase 208 volt 3 hp motor with a NEMA Size 1 contactor with a 208 volt coil and a start/stop built in.
After the initial smoking of the coil, it had a 24volt coil instead of the 208 volt varity the box label stated. Lesson learned...
Anyway, I now have the correct coil but it won't pull in, it chatters. I read the voltage to actually be about 225 volts between phases which is not something I have come across much in this neighborhood.
Is there a "range" that the coil should work in? This started as a simple "favor" for a friend and it is turning into more of a time consuming problem.
Any input is appreciated.

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#184847 - 02/23/09 06:42 PM Re: 208 volt contactor [Re: rcksmith127]
ghost307 Offline
Member

Registered: 05/09/05
Posts: 877
Loc: Chicago Illinois USA
Chattering is often the result of installing a DC coil on an AC control circuit.
When the drops to zero (before reversing polarity) the coil loses its field and the contactor starts to spring back open.
_________________________
Ghost307

Top
#184848 - 02/23/09 06:44 PM Re: 208 volt contactor [Re: rcksmith127]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9012
Loc: Estero,Fl,usa
Is this the type with a pick and hold coil, selected by a side switch? You may be wired to the hold side.
_________________________
Greg Fretwell

Top
#184854 - 02/23/09 08:08 PM Re: 208 volt contactor [Re: rcksmith127]
smokey Offline
Member

Registered: 04/06/01
Posts: 42
Loc: cctxusa
i am experiencing the same problem with a set of contactors that control heating elements for a water heater.they keep chattering .even after replacement.i am now in the process of replacing them with a larger contactor 70a instead of 50a .i am thinking that the load is to much for the contactor.im not sure if this is helpful to you.im not sure if the higher voltage would effect the contacts inside the contactor.

Top
#184857 - 02/23/09 09:01 PM Re: 208 volt contactor [Re: smokey]
JBD Offline
Member

Registered: 07/12/01
Posts: 599
Loc: WI, USA
Load does not affect the contactor sealing in.

The three most common reasons that contactors make noise are:
Low coil voltage. Most coils will pull in at 85% and drop out at 65%.
Jammed mechanism from dust or worn slides.
And probably the most common; rust, dirt, or scratches on the magnet poles faces which prevent them from mating correctly.

Top
#184860 - 02/24/09 06:02 AM Re: 208 volt contactor [Re: JBD]
SteveFehr Offline
Member

Registered: 03/19/05
Posts: 1192
Loc: Chesapeake, VA
It could simply be defective from the factory. We ran into a few defective chattering contactor solenoids last year in an application where problems like that are unheard of (high-end UPS systems).

It can be hard to tell the difference between a wrong part and a defective one, especially if you're pulling the replacements from the same defective batch.

Top
#184877 - 02/24/09 04:33 PM Re: 208 volt contactor [Re: SteveFehr]
JBD Offline
Member

Registered: 07/12/01
Posts: 599
Loc: WI, USA
One more question.

You say it does not pull in, it just chatters.
Do you mean that it chatters while you hold the Start button in and then it drops out when you release the button?
Not holding in would be caused by a bad holding circuit contact or a wiring error.
Chattering, like rapid pickup then dropout, could be a wiring error where a contact from the starter is actually turning the circuit off instead of holding the circuit on.

Top
#184880 - 02/24/09 06:24 PM Re: 208 volt contactor [Re: JBD]
mb95307 Offline
New Member

Registered: 05/02/08
Posts: 4
Loc: Ceres, CA
Most contactors are equiped with a shaded pole. This shaded pole holds the contactor shut while the AC current crosses the zero point. If it is chattering, this is the first thing that I would look for...

Top
#184881 - 02/24/09 06:26 PM Re: 208 volt contactor [Re: mb95307]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9012
Loc: Estero,Fl,usa
got my attention...
_________________________
Greg Fretwell

Top
#184890 - 02/25/09 05:39 AM Re: 208 volt contactor [Re: mb95307]
SteveFehr Offline
Member

Registered: 03/19/05
Posts: 1192
Loc: Chesapeake, VA
Originally Posted By: mb95307
Most contactors are equiped with a shaded pole. This shaded pole holds the contactor shut while the AC current crosses the zero point. If it is chattering, this is the first thing that I would look for...
How does that work, are there two solenoids in the contactor, one with a straight winding and one with a shaded pole?

Top