#184631 - 02/14/09 08:25 PM Disconnect at secondary of transformer
Rhiney Offline
New Member
Registered: 02/12/09
Posts: 3
Loc: California
Hello there!
I've got a situation here where we are setting a 112.5kva480x 120/208 transformer on the roof of a building.
It will supply power to a 400Amp MCB-type panelboard below roughly 40'of conduit and wire away.
Are we required to have a fused disconnect near the transformer (word has it wthin 25')? Where in the code is this requirement if it exists?
Primary overcurrent protection is a 175amp circuit breaker.
Thanks much for any help
Top
2017 / 2014 NEC & Related Books and Study Guides
#184632 - 02/14/09 08:41 PM Re: Disconnect at secondary of transformer [Re: Rhiney]
Yoopersup Offline
Member
Registered: 03/04/03
Posts: 822
Loc: Michigan
240.21
Read which one applys in this section for you.
Also read Table 450.3(B).


Edited by Yoopersup (02/14/09 08:44 PM)
Top
#184633 - 02/14/09 09:41 PM Re: Disconnect at secondary of transformer [Re: Yoopersup]
Rhiney Offline
New Member
Registered: 02/12/09
Posts: 3
Loc: California
Thanks much Yoopersup.
That cleared it right up for me . A fused disconnect within 25ft it is .
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6776
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (gfretwell), 48 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals