The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 10
Texas_Ranger 8
Trumpy 8
sparkyinak 7
Who's Online
1 registered (LongRunner), 206 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#184569 - 02/13/09 09:53 AM Grounding electrode from inside subpanel??
sparkync Offline
Member

Registered: 10/17/02
Posts: 811
Loc: NC
I recently changed a service from 100 amps to 200 amps. The inside panel had a ground wire going to the water pipe. This panel is not located with the mains outside. Can I leave this ground wire hooked up or do I disconnect it? I have the grounding electrode outside connectected to the Main panel outside. Thanks... Steve

Top
2014 / 2011 NEC & Related Books and Study Guides
#184574 - 02/13/09 10:10 AM Re: Grounding electrode from inside subpanel?? [Re: sparkync]
frenchelectrican Offline

Member

Registered: 02/06/03
Posts: 938
Loc: Wi/ Paris France { France for ...
For myself I will leave it and that panel become a subpanel so as long you have grouding bar in there and keep the netrual and ground seprated and the exsting EGC is there you can use it.

{ unless your local code say something diffrent then follow thier regualtions }

Merci,Marc
_________________________
Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)


Top
#184575 - 02/13/09 10:11 AM Re: Grounding electrode from inside subpanel?? [Re: sparkync]
leland Offline
Member

Registered: 08/20/07
Posts: 856
Loc: Lowell area, Ma. USA
Metal main water pipe?
What is your main ground electrode now?
Either way, the copper water pipe must be bonded.

sounds like your ok, bond the pipe to the Subs ground.Jump the meter so you have a good bond on the house side.

250.52 addresses this.


Edited by leland (02/13/09 10:13 AM)
Edit Reason: water meter jumper

Top
#184580 - 02/13/09 02:04 PM Re: Grounding electrode from inside subpanel?? [Re: sparkync]
KJay Offline
Member

Registered: 11/27/07
Posts: 763
Loc: MA, USA
Originally Posted By: sparkync
I recently changed a service from 100 amps to 200 amps. The inside panel had a ground wire going to the water pipe. This panel is not located with the mains outside. Can I leave this ground wire hooked up or do I disconnect it? I have the grounding electrode outside connectected to the Main panel outside. Thanks... Steve


I think the problem might be that if it was previously 100A, then that bond to the water piping is probably only a #6 or #8 Cu.
With a 200A, it now should be at least #4, according to Table 250.66.
I would remove the old wire and run a new #4 Cu from the piping to the main panel outside. IMO, that's where it really belongs anyway.

Top
#184581 - 02/13/09 04:10 PM Re: Grounding electrode from inside subpanel?? [Re: KJay]
leland Offline
Member

Registered: 08/20/07
Posts: 856
Loc: Lowell area, Ma. USA
K-Jay- hello.

At this point providing he met the proper GEC methods. Isn't this just now a bond?

Top
#184585 - 02/13/09 05:31 PM Re: Grounding electrode from inside subpanel?? [Re: leland]
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 826
Loc: Michigan
Kjay is Right your grounding electroid wire at the outside 100 is probally 6 or 8.
You need a #4 for 200 amps . (250.66)
This MUST be run to the Service disconnecting means outside Not subpanel. (250.24C).
Also read (250.50)250.52)
Yoopersup

Top
#184586 - 02/13/09 06:01 PM Re: Grounding electrode from inside subpanel?? [Re: Yoopersup]
leland Offline
Member

Registered: 08/20/07
Posts: 856
Loc: Lowell area, Ma. USA
If the water main is primary, then a supplemental GE is needed.
My understanding is He has his ground (thru rods) met.Now the water need only be bonded.

Top
#184587 - 02/13/09 06:33 PM Re: Grounding electrode from inside subpanel?? [Re: leland]
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 826
Loc: Michigan
250.50
ALL grounding electrodes as described in 250.52(a)1 though (a)6 that are PRESENT. shall be bonded TOGETHER to form grounding electrod system.
See 250.52 Water Underground Water pipeing.
Your only bonding the water line when less then 10ft of metal pipe is outside the building.
Again read code sections I refered to in my ist post.
Yoopersup
If its part of the Grounding Electrod system it must go to the Service disconnect or disconnect switches.

Top
#184588 - 02/13/09 06:55 PM Re: Grounding electrode from inside subpanel?? [Re: Yoopersup]
leland Offline
Member

Registered: 08/20/07
Posts: 856
Loc: Lowell area, Ma. USA
Originally Posted By: Yoopersup
250.50
ALL grounding electrodes as described in 250.52(a)1 though (a)6 that are PRESENT. shall be bonded TOGETHER to form grounding electrod system.
See 250.52 Water Underground Water pipeing.
Your only bonding the water line when less then 10ft of metal pipe is outside the building.
Again read code sections I refered to in my ist post.
Yoopersup
If its part of the Grounding Electrod system it must go to the Service disconnect or disconnect switches.


Got Me Guy!!!
"..That are present...."
Up size it and bring that conductor back to the main.

Thanx for grabbing my attention to that.I got tunnel vision.

Top
#184592 - 02/13/09 07:27 PM Re: Grounding electrode from inside subpanel?? [Re: Yoopersup]
renosteinke Offline
Cat Servant
Member

Registered: 01/22/05
Posts: 5305
Loc: Blue Collar Country
Look at 250.66 closer ... the text, not the table. You need not have a GEC larger than #6, no matter the service size.