The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
Yesterday at 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
0 registered (), 107 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#184402 - 02/09/09 02:10 PM NM Protection - Exposed Work
InspectorE Offline
Member

Registered: 10/08/04
Posts: 51
Loc: Hudson WI USA
Section 334.16(b)requires that NM used in exposed areas be protected with conduit or other approved means. Does the code indicate minimum diameters for various NM sizes similar to the conduit fill tables? Or is the amount of space taken up by the NM irrelevant with respect to conduit diameter? If so is it left to the installer's judgement?

Top
2014 / 2011 NEC & Related Books and Study Guides
#184403 - 02/09/09 02:11 PM Re: NM Protection - Exposed Work [Re: InspectorE]
InspectorE Offline
Member

Registered: 10/08/04
Posts: 51
Loc: Hudson WI USA
That should be 334.15(b), not 16..typo

Top
#184405 - 02/09/09 02:43 PM Re: NM Protection - Exposed Work [Re: InspectorE]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
You use the circular size defined by the widest dimension of the cable. For flat Romex that makes a pretty fat "conductor". A 12-2 is about .4" which puts it between a #2 and a #1 THHN. Generally I will make some concession if this is a single straight run down a wall.
_________________________
Greg Fretwell

Top
#184409 - 02/09/09 04:07 PM Re: NM Protection - Exposed Work [Re: gfretwell]
LK Offline

Member

Registered: 01/21/03
Posts: 1721
Loc: New Jersey
Yup, it's all spelled out in the code.