The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
10/24/16 08:46 PM
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 7
ghost307 7
renosteinke 6
Potseal 4
Who's Online
0 registered (), 340 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#184402 - 02/09/09 02:10 PM NM Protection - Exposed Work
InspectorE Offline

Registered: 10/08/04
Posts: 51
Loc: Hudson WI USA
Section 334.16(b)requires that NM used in exposed areas be protected with conduit or other approved means. Does the code indicate minimum diameters for various NM sizes similar to the conduit fill tables? Or is the amount of space taken up by the NM irrelevant with respect to conduit diameter? If so is it left to the installer's judgement?

2014 / 2011 NEC & Related Books and Study Guides
#184403 - 02/09/09 02:11 PM Re: NM Protection - Exposed Work [Re: InspectorE]
InspectorE Offline

Registered: 10/08/04
Posts: 51
Loc: Hudson WI USA
That should be 334.15(b), not 16..typo

#184405 - 02/09/09 02:43 PM Re: NM Protection - Exposed Work [Re: InspectorE]
gfretwell Offline


Registered: 07/20/04
Posts: 9026
Loc: Estero,Fl,usa
You use the circular size defined by the widest dimension of the cable. For flat Romex that makes a pretty fat "conductor". A 12-2 is about .4" which puts it between a #2 and a #1 THHN. Generally I will make some concession if this is a single straight run down a wall.
Greg Fretwell

#184409 - 02/09/09 04:07 PM Re: NM Protection - Exposed Work [Re: gfretwell]
LK Offline


Registered: 01/21/03
Posts: 1721
Loc: New Jersey
Yup, it's all spelled out in the code.