The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
230 or 345 kV transmission lines?
by Vlado
09/24/16 09:33 AM
breaker meltdown
by crselectric
09/24/16 12:42 AM
Electrical mast flashing product
by ThomasWinfrey
09/22/16 12:14 AM
What estimating software do you recommend?
by sparky
09/21/16 07:20 PM
"Dry Run" Inspection goes awry
by HotLine1
09/20/16 07:39 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 15
sparky 9
gfretwell 8
sparky66wv 8
Vlado 6
Who's Online
1 registered (Icarus), 159 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#183727 - 01/20/09 06:48 PM "Bubble" receptacle cover
leland Offline
Member

Registered: 08/20/07
Posts: 856
Loc: Lowell area, Ma. USA
If I install a receptacle in a car wash bay, or A medical research lab area (with water around Wet location).

Do I need one?

Top
2014 / 2011 NEC & Related Books and Study Guides
#183729 - 01/20/09 06:56 PM Re: "Bubble" receptacle cover [Re: leland]
renosteinke Offline
Cat Servant
Member

Registered: 01/22/05
Posts: 5299
Loc: Blue Collar Country
Yes. The 'industrial' exception has been tightened up considerably. That's the code.

Realistically though .... the one in the car wash is going to be busted off within minutes of your leaving. I'd rather see an intact weather cover, than a broken bubble cover.

As for the research lab ... I'd go the extra mile, gat a metal one, and use tamper-resistant screws. Those dweebs love to play around.

Top
#183735 - 01/20/09 09:45 PM Re: "Bubble" receptacle cover [Re: renosteinke]
leland Offline
Member

Registered: 08/20/07
Posts: 856
Loc: Lowell area, Ma. USA
Originally Posted By: renosteinke
Yes. The 'industrial' exception has been tightened up considerably. That's the code.


406.8(B)(1) Exception: Has changed?

406.8(B)(2)(b). could I not say that an outside rec on a dwelling is for a weed whacker? therefor not needing a 'bubble' cover?

406.8(A)- covered porch no 'bubble' required? Inspectors demand it (am I wrong?).

Top
#183947 - 01/28/09 09:57 AM Re: "Bubble" receptacle cover [Re: leland]
Tom Offline
Member

Registered: 01/01/01
Posts: 1069
Loc: Shinnston, WV USA
Leland,

406.8(B)(1) exception is new and IMO allows you to get away from the bubble cover in a car wash even though you are not high pressure washing the wall or receptacle cover. I could be all wet in my understanding of this. Also, there are metal bubble covers on the market.

406.8(B)(2) applies to receptacles other than the ones in (B)(1) such as a 30 amp or larger receptacle.

Lastly, I've always had problems with damp locations. I've never seen a really good definition of a damp location. How far back under the porch roof is the receptacle? If the AHJ feels that the wind could blow rain back that far, then it is a wet location. I've always stuck to the 45 degree installation. If you draw a line extending back from the edge of the roof 45 degrees and the outlet or other equipment is above the line, it is a damp location, below the line a wet location. If the wind is strong enough to blow the rain at a greater angle, a bubble cover is the least of your worries.

Tom
_________________________
Few things are harder to put up with than the annoyance of a good example.

Top
#183949 - 01/28/09 11:05 AM Re: "Bubble" receptacle cover [Re: Tom]
SteveFehr Offline
Member

Registered: 03/19/05
Posts: 1192
Loc: Chesapeake, VA
But where do you plug in your pressure washer??

Assume for a moment you want to "exceed" the code and put in a bubble. A standard bubble wouldn't work here, and would just create false confidence. It would have to be a NEMA-4X bubble; do they even exist?

Top
#183953 - 01/28/09 04:59 PM Re: "Bubble" receptacle cover [Re: SteveFehr]
Tom Offline
Member

Registered: 01/01/01
Posts: 1069
Loc: Shinnston, WV USA
The OP didn't state if the car wash bay was a typical coin operated installation. If it is coin operated, the pressure pump is usually hard wired and located in a dry location.

If you're plugging in a pressure washer & are concerned about the receptacle getting soaked, install a pendant receptacle that has rubber boots that seal the connectors when you're plugged in.

Regardless of what you do, sooner or later some bonehead is going to see if that wet location connection can withstand the 3500 + psi that these things can put out.
_________________________
Few things are harder to put up with than the annoyance of a good example.

Top
#183965 - 01/28/09 09:19 PM Re: "Bubble" receptacle cover [Re: Tom]
leland Offline
Member

Registered: 08/20/07
Posts: 856
Loc: Lowell area, Ma. USA
Re-Read- 406.8(B)- Bubble is required.
The Exception is not needed.
Heck, If your plugged in you need a WP cover,If not, WP cover still needed. ...??...

Top
#183970 - 01/29/09 12:12 AM Re: "Bubble" receptacle cover [Re: SteveFehr]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9012
Loc: Estero,Fl,usa
Pressure washer plugs usually have built in GFCIs. I have never seen a bubble that would hold one and still close.
_________________________
Greg Fretwell

Top
#183974 - 01/29/09 07:08 AM Re: "Bubble" receptacle cover [Re: gfretwell]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6785
Loc: Brick, NJ USA
Greg:
With due respect, my pressure washer has a GFI in the cord, approx. 18" from the male cap.
_________________________
John

Top
#183986 - 01/29/09 12:28 PM Re: "Bubble" receptacle cover [Re: HotLine1]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9012
Loc: Estero,Fl,usa
My 5 HP washer (30a 240v) has that in the cord but the 120v baby pressure washer has it in the plug.
_________________________
Greg Fretwell

Top
Page 1 of 2 1 2 >



ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals