#183395 - 01/07/09 10:40 PM Fried Outlet
Webmaster Offline

Administrator
Member

Registered: 10/07/00
Posts: 3142
Loc: NY, USA
Quote:
I came across this awhile back in a gift shop store in the area I live in. The woman told me it was the result of a malfunctioning space heater; there is a second outlet next to this one that was installed to replace the burnt one here. The burnt one is no longer used.

Tristan S.


Top
2014 / 2011 NEC & Related Books and Study Guides
#183404 - 01/08/09 11:39 AM Re: Fried Outlet [Re: Webmaster]
mikesh Offline
Member

Registered: 06/07/06
Posts: 614
Loc: Victoria, BC, Canada
Do you mean that instead of replacing that receptacle the shop ran a new circuit? Maybe they tapped the new plug off the same circuit ;-)

Top
#183423 - 01/08/09 07:22 PM Re: Fried Outlet [Re: mikesh]
noderaser Offline
Member

Registered: 03/01/07
Posts: 405
Loc: Portland, Oregon, United State...
Why would you want to keep something like that? To me it is a warning sign, to know where the exits are in the building in case anything else decides to burst into flames.


Edited by noderaser (01/08/09 07:24 PM)
_________________________
http://www.hsiprodsvcs.com/

Top
#183440 - 01/09/09 04:51 AM Re: Fried Outlet [Re: noderaser]
ComputerWizKid Offline
Member

Registered: 09/20/03
Posts: 116
Loc: Connecticut, USA
I hope that outlet was originally brown and not burnt so bad that it turned that color
_________________________
Theres always enough room in the junction box.You just need a bigger hammer

Top
#183441 - 01/09/09 10:00 AM Re: Fried Outlet [Re: ComputerWizKid]
packrat56 Offline
Member

Registered: 03/03/08
Posts: 76
Loc: MT, U.S.
To be honest mikesh, I don't know. They probably ended up using the same cable run if it was still good. The only sources of heat used to keep the place warm are space heaters, which I'm sure operating continuously at least most of time.
_________________________
I have a sense of adventure, I just keep it leashed with common sense.

Top
#183449 - 01/09/09 05:20 PM Re: Fried Outlet [Re: packrat56]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6804
Loc: Brick, NJ USA
Packrat56:
Are you saying that the only heat in a retail store is a 120 volt, plug-in space heat??

You are in Montana, Right? Sounds like a place that gets brutally cold to me.

A store that used portable space heaters for there only heat would get shut down by the Fire Dept here, unless it was an emergency situation, and then only for a very limited time frame.
_________________________
John

Top
#183475 - 01/10/09 06:16 PM Re: Fried Outlet [Re: HotLine1]
packrat56 Offline
Member

Registered: 03/03/08
Posts: 76
Loc: MT, U.S.
Actually, now that I think about it HotLine1 they must have furnace system, given the size of the place I don't see how the space heaters can keep up because it does get pretty cold where I live. I've seen days where the highest temperature of the day doesn't even get above 0 degrees on the Fahrenheit scale. So the space heaters just provide additional as needed. I apologize for the misinformation.


Edited by packrat56 (01/10/09 06:18 PM)
_________________________
I have a sense of adventure, I just keep it leashed with common sense.

Top
#183504 - 01/11/09 06:43 PM Re: Fried Outlet [Re: packrat56]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6804
Loc: Brick, NJ USA
Apology is not necessary! No misinformation! I ask a lot of questions, and if my wording seemed strong....it was not meant that way.
_________________________
John

Top
#183507 - 01/11/09 07:30 PM Re: Fried Outlet [Re: HotLine1]
Lostazhell Offline
Member

Registered: 02/21/04
Posts: 1248
Loc: Bakersfield, CA (Originally Or...
Slater doesn't get a lot of good press around here laugh

Burnt Receptacle

Seeing the blown off prong stuck in the outlet still almost makes me think something metal fell in between the outlet and the (former) plug and OCPD didn't trip quite instantly... The faceplate looks to have gotten very hot at the top yoke area also..

Top
#183559 - 01/14/09 12:48 PM Re: Fried Outlet [Re: Lostazhell]
mamills Offline
Member

Registered: 11/30/01
Posts: 739
Loc: Wharton, Texas, USA
A couple of red flags pop up here. I would certainly check to be sure that this rect. is permanently rendered dead, or else replaced with something of better quality once its wiring is inspected and/or replaced as well. Just the sight of something like that gives me the creeps. I know they need to keep the place warm, but the idea of leaving operating space heaters in a store after hours is an invitation to the fire department.

Randy has a good eye. The burn pattern on the top of that plate certainly suggests something that may have fallen across the heater connector.

Mike (Mamills)


Edited by mamills (01/14/09 12:54 PM)

Top