The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Locked rotor, no burnout
by andey
Yesterday at 04:48 AM
Temporarily feeding a panel...
by Potseal
09/29/16 11:05 PM
Massive power outage South Australia
by Meadow
09/29/16 06:46 AM
short circuit??
by Meadow
09/29/16 06:43 AM
Norwegian power?
by Meadow
09/29/16 06:36 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 12
sparky 10
gfretwell 8
Potseal 7
sparky66wv 6
Who's Online
0 registered (), 289 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#183248 - 01/01/09 09:41 AM Ice Storm Surge?
Merlin Offline
Member

Registered: 01/27/04
Posts: 170
Loc: NW Indiana
I was called to residence yesterday to do an inspection of damage for the insurance company. We recently had an ice storm that took down power lines. This customer was out for 4 days. When his power came back on, he had multiple items burnt up. Micro, stove, cordless phone, dishwasher, tv, vcr, dvd player, computer surge protector, flourescent lights to name a few. The major items didn't get affected because he had them unplugged and plugged into a generator.

The odd thing about this is everthing affected was on the same phase in his (120/240) panel. Now I have seen this before on a phase to neutral short on an overhead service. But his service is all underground from the transformer pole to his house. The cause of the outage was a primary line broke a mile down the road.

Can anybody give me an explanation for this?

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#183249 - 01/01/09 10:21 AM Re: Ice Storm Surge? [Re: Merlin]
jdevlin Offline
Member

Registered: 08/07/02
Posts: 402
Loc: welland ontario canada
Did the primary break and drop onto the one line feeding into the house? Maybe it dropped onto the line at someone else's house and backfed his house.


Edited by jdevlin (01/01/09 10:22 AM)

Top
#183251 - 01/01/09 10:31 AM Re: Ice Storm Surge? [Re: jdevlin]
JValdes Offline
Member

Registered: 06/03/07
Posts: 308
Loc: South Carolina
I would consider everything you stated as "major items".
Sorry I have no decent idea as to what might have happened. Make something up (blame POCO)and be done with it.

Top
#183254 - 01/01/09 10:46 AM Re: Ice Storm Surge? [Re: JValdes]
Tom Offline
Member

Registered: 01/01/01
Posts: 1069
Loc: Shinnston, WV USA
The only thing I can think of that wasn't covered would be a loose neutral. Many of the items you mentioned are electronic or contain electronics . Electronics don't much care for high voltage. Did you take any voltage measurements while you were on site?
_________________________
Few things are harder to put up with than the annoyance of a good example.

Top
#183259 - 01/01/09 11:49 AM Re: Ice Storm Surge? [Re: Tom]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9012
Loc: Estero,Fl,usa
Were the other homes on that transformer affected?
I doubt the PoCo will do anything but it might help with the insurance company.
_________________________
Greg Fretwell

Top
#183261 - 01/01/09 12:47 PM Re: Ice Storm Surge? [Re: jdevlin]
Merlin Offline
Member

Registered: 01/27/04
Posts: 170
Loc: NW Indiana
Originally Posted By: jdevlin
Did the primary break and drop onto the one line feeding into the house? Maybe it dropped onto the line at someone else's house and backfed his house.


No that was not possible. The primary that broke was a mile down the road. And no I don't believe that it could have back feed because this is the only house on this transformer. The transformer pole is only 45' from his house. The secondary comes down the transformeer pole underground to his house.

Top
#183269 - 01/01/09 07:04 PM Re: Ice Storm Surge? [Re: Merlin]
pdh Offline
Member

Registered: 01/20/05
Posts: 354
If there were no wires down in that entire mile from the primary down to his house, that primary down will be the biggest suspect culprit. Still, it is hard to imagine it causing the surge to extend to your customer's house unless there were secondaries run the whole way (which you say is not the case).

Any overvoltage on the primary would have affected both 120 phases and everything 240. If all the damage is on one 120 phase, that sounds to me more like an arc-over in the transformer, or a fault of the other phase to neutral somewhere.

I suggest a test. Find another surge protector exactly like the one that failed. Apply 240 volts to it and see if it fails. Some will and some won't. If it does not fail, then there had to be more than 240 volts.

A closer inspection of damage to appliances might give a better idea of what the voltage involved was. Any change it might have been an UNDERvoltage issue?

Did the homeowner report any lightning events? I have experienced lightning in snow and ice storms before (but luckily was not hit by it).

Top
#183271 - 01/01/09 07:39 PM Re: Ice Storm Surge? [Re: pdh]
Merlin Offline
Member

Registered: 01/27/04
Posts: 170
Loc: NW Indiana
My first thought when I got the phone call was an undervoltage. This seems to happen frequently in these type of storms. However upon inspection, it is all on the same phase and shows sign of an extensive surge. The next scenario is lightning. There were some thunderstorms reported in the area, however I never saw any. That is the only case that I can see but the homowner says that he didn't see any.

My next step is to talk to PoCo and have them check the transformer and connections. I am also going to recheck all secondary connections for loose neutrals, ect.

Top
#183273 - 01/01/09 10:35 PM Re: Ice Storm Surge? [Re: Merlin]
Rewired Offline
Member

Registered: 01/01/06
Posts: 567
Loc: Hamilton, Ontario, Canada
Question: Is the wire that came down the same phase as the one supplying the transformer?? If they are different phases, and the transformer primary is connected line-neutral, and say the neutral has a poor connection in it somewhere or is undersized, would it not be possible the transformer saw a momentary overvoltage if the downed wire contacted the primary neutral or the fault current tried to return through the primary neutral?? For a brief time that transformer primary would have a voltage across it somewhere between the line-neutral and line-line voltages, at least until the primary fuses opened up would it not???
I would think that would cause enough of a voltage rise in the secondary to burn things up..

A.D

Top
#183277 - 01/02/09 12:26 AM Re: Ice Storm Surge? [Re: JValdes]
Trumpy Offline

Member

Registered: 07/05/02
Posts: 8530
Loc: SI,New Zealand
Originally Posted By: JValdes
I would consider everything you stated as "major items".
Sorry I have no decent idea as to what might have happened. Make something up (blame POCO)and be done with it.

So, you have no real idea as to what might have occured, but you are willing for this guys customer to lie to the PoCo.
That is called Fraud.

Why is it always the PoCo's problem?
Home-owners should have their own Surge Diversion equipment, installed in THEIR panels if they have sensitive gear that might be cooked by voltage surges.
I'm all for personal responsibility.
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin

Top