The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Locked rotor, no burnout
by andey
Today at 04:48 AM
Temporarily feeding a panel...
by Potseal
Yesterday at 11:05 PM
Massive power outage South Australia
by Meadow
Yesterday at 06:46 AM
short circuit??
by Meadow
Yesterday at 06:43 AM
Norwegian power?
by Meadow
Yesterday at 06:36 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 14
sparky 10
gfretwell 8
sparky66wv 8
Potseal 7
Who's Online
1 registered (jraef), 292 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#183211 - 12/31/08 08:09 AM hospital iso panels?
allphase Offline
Member

Registered: 09/05/07
Posts: 14
Loc: Chicago il.
happy new year all.

Got in to some thing the other day. looking for info.
are isolation panel still required in surgegy recovery rooms? and if so or not where in the code have thay been removed or that thay need to be there

any help would bee nice i have looked thru 517 and can not find any thing on it.

thanks larry

Top
2014 / 2011 NEC & Related Books and Study Guides
#183220 - 12/31/08 10:10 AM Re: hospital iso panels? [Re: allphase]
renosteinke Offline
Cat Servant
Member

Registered: 01/22/05
Posts: 5300
Loc: Blue Collar Country
Such a requirement is a design decision, not a code one. Strictly speaking, the NEC doesn't mandate such things; it only allows other rules to be waived if such is present.

Medical facilities have all manner of 'special' needs these days. Not only is there the desire not to ignite anesthetic vapors, there are back-up power and ground fault protection decisions to be made. Then there's that whole 'equipotential plane' thing ....

In short, this is where the engineer or architect has to actually do some work, and not foist it all off on the trades to sort out.

Top
#183225 - 12/31/08 12:54 PM Re: hospital iso panels? [Re: renosteinke]
ghost307 Offline
Member

Registered: 05/09/05
Posts: 877
Loc: Chicago Illinois USA
We went around and around with this question for several hospital projects that I worked on.

The NEC only tells you HOW you need install this...not whether or not you need it.

Reviewing the rest of the 'tons' of Codes that apply to Health Care, the end result is that they aren't required by the letter of the law, although having them (IMHO) is an excellent idea.

Like with most things in this world...it always came down to the money. If it wasn't "required", the folks with the checkbooks saw no need to "waste good money" on them; no matter if they were recommended or not.
_________________________
Ghost307

Top
#183322 - 01/04/09 12:06 PM Re: hospital iso panels? [Re: ghost307]
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 826
Loc: Michigan
There are Three Major areas in a Hospital.
Critical, General, Wet.
Critical General you can use GFI (lost of power can be tolerated),
Critical WET (Lost of power Cannot be tolerated(possibly cause a lose of life)Isolated power System required.
All areas to be desiginated by hospital Administerer (see definitations 517)
See 517.20 A Wet Locations.Receptacles & Fixed Equipment.