The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
10/24/16 08:46 PM
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 7
ghost307 7
renosteinke 6
Potseal 4
Who's Online
0 registered (), 268 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#183123 - 12/27/08 10:50 AM Generator interface
leland Offline

Registered: 08/20/07
Posts: 856
Loc: Lowell area, Ma. USA
I hope all are haveing a great Holiday season! The best for the New Year!

Now, After the rash of bad weather here and the power outages, I've had a lot of calls for The manual transfers for Portable Generators.I use 10 ckt panels.
Most are straight forward- Prewired nippled to the panel-10/3 to the garage and an outside box.
Yesterday I ran across an elderly lady who does not want to go to the basement to turn them on.
So my thought is to place the switch in the garage.
How ever this would require 20 12s' in conduit (switch legs)Up the neutral to #8.
As most will know the prewired (240/120-30A)comes with a flex,20 leads and #10 neutral and ground.
IMO, this would be just an extension of the factory set up,But still makes me question my thoughts.
Any ideas? confirmations,or potential problems?
Tanx, Lee

Edited by leland (12/27/08 10:51 AM)

Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#183128 - 12/27/08 11:38 AM Re: Generator interface [Re: leland]
sparkyinak Offline

Registered: 07/08/07
Posts: 1288
Loc: Alaska
First question, are you under the 2008 NEC?
"Live Awesome!" - Kevin Carosa

#183131 - 12/27/08 12:11 PM Re: Generator interface [Re: sparkyinak]
leland Offline

Registered: 08/20/07
Posts: 856
Loc: Lowell area, Ma. USA

#183132 - 12/27/08 02:19 PM Re: Generator interface [Re: leland]
renosteinke Offline
Cat Servant

Registered: 01/22/05
Posts: 5305
Loc: Blue Collar Country
You don't have a lot of room within the transfer switch enclosure, nor is there much space under the screws / clamps that the wires attach to.

I would suggest mounting a fairly large can, or even a small gutter, near the transfer switch. I'd then terminate the wires to a terminal stirp, and connect the "extension wires" there. I'd rather do this than use wire nuts.

Though ... all considered .... 10 circuits is a fairly large number, and with the matter of convenience added in ... perhaps we would be better served by re-doing the arrangement completely, perhaps with a sub-panel and an automatic transfer switch.

It comes down to the "cheap-good-fast" riddle. The original was cheap and fast, but not that good. There's no way around that!

#183136 - 12/27/08 06:21 PM Re: Generator interface [Re: renosteinke]
leland Offline

Registered: 08/20/07
Posts: 856
Loc: Lowell area, Ma. USA

Similar to this.
All self contained. in that whip is a #10 neutral and ground.10 ckt switch legs.
The generator plugs into the front.
Red wires to breaker and black wires to load. Very slick set up. Neutral to the N buss and ground of course.
typically loads are spliced in the panel. This application I was thinking about moving this T-switch to the garage,Effectively just extending the switch legs.
Terminal strip is in order,Yes.

Edited by leland (12/27/08 06:22 PM)