#183123 - 12/27/08 10:50 AM Generator interface
leland Offline
Member
Registered: 08/20/07
Posts: 856
Loc: Lowell area, Ma. USA
I hope all are haveing a great Holiday season! The best for the New Year!

Now, After the rash of bad weather here and the power outages, I've had a lot of calls for The manual transfers for Portable Generators.I use 10 ckt panels.
Most are straight forward- Prewired nippled to the panel-10/3 to the garage and an outside box.
Yesterday I ran across an elderly lady who does not want to go to the basement to turn them on.
So my thought is to place the switch in the garage.
How ever this would require 20 12s' in conduit (switch legs)Up the neutral to #8.
As most will know the prewired (240/120-30A)comes with a flex,20 leads and #10 neutral and ground.
IMO, this would be just an extension of the factory set up,But still makes me question my thoughts.
Any ideas? confirmations,or potential problems?
Tanx, Lee


Edited by leland (12/27/08 10:51 AM)
Top
Work Gear for Electricians and the Trades
#183128 - 12/27/08 11:38 AM Re: Generator interface [Re: leland]
sparkyinak Offline
Member
Registered: 07/08/07
Posts: 1309
Loc: Alaska
First question, are you under the 2008 NEC?
_________________________
"Live Awesome!" - Kevin Carosa
Top
#183131 - 12/27/08 12:11 PM Re: Generator interface [Re: sparkyinak]
leland Offline
Member
Registered: 08/20/07
Posts: 856
Loc: Lowell area, Ma. USA
08,Yes
Top
#183132 - 12/27/08 02:19 PM Re: Generator interface [Re: leland]
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5305
Loc: Blue Collar Country
You don't have a lot of room within the transfer switch enclosure, nor is there much space under the screws / clamps that the wires attach to.

I would suggest mounting a fairly large can, or even a small gutter, near the transfer switch. I'd then terminate the wires to a terminal stirp, and connect the "extension wires" there. I'd rather do this than use wire nuts.

Though ... all considered .... 10 circuits is a fairly large number, and with the matter of convenience added in ... perhaps we would be better served by re-doing the arrangement completely, perhaps with a sub-panel and an automatic transfer switch.

It comes down to the "cheap-good-fast" riddle. The original was cheap and fast, but not that good. There's no way around that!
Top
#183136 - 12/27/08 06:21 PM Re: Generator interface [Re: renosteinke]
leland Offline
Member
Registered: 08/20/07
Posts: 856
Loc: Lowell area, Ma. USA
http://www.northerntool.com/webapp/wcs/stores/servlet/product_6970_200321033_200321033

Similar to this.
All self contained. in that whip is a #10 neutral and ground.10 ckt switch legs.
The generator plugs into the front.
Red wires to breaker and black wires to load. Very slick set up. Neutral to the N buss and ground of course.
typically loads are spliced in the panel. This application I was thinking about moving this T-switch to the garage,Effectively just extending the switch legs.
Terminal strip is in order,Yes.


Edited by leland (12/27/08 06:22 PM)
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
License exam
by TRUE POWER
01/23/17 09:16 PM
Looking for older post
by sparkyinak
01/23/17 12:27 AM
Members: Non-Members: Did you know?
by Admin
01/22/17 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM
International Wire Colour Codes
by Texas_Ranger
01/21/17 03:29 PM

Who's Online
1 registered (Admin), 72 Guests and 12 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Member Since: 11/11/05
Posts: 190

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals