The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
International Wire Colour Codes
by Texas_Ranger
Today at 08:24 AM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
230 or 345 kV transmission lines?
by annemarie1
10/12/16 01:23 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 11
renosteinke 6
HotLine1 6
ghost307 5
Potseal 4
Who's Online
1 registered (Tjia1981), 182 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#183020 - 12/21/08 10:06 PM Florescent lights
schenimann Offline

Registered: 02/18/08
Posts: 194
Loc: Western North Carolina
We put up 158 florescent lights in commercial job. They all work from two switches through contactors. I was in a j box hooking up a emergency light with the breakers off for the emergency circuit. Realized that I had 120v from neutral to ground. I traced it to a row of lights.

I have a row of about 13 8ft t8 fixtures. I have a whip that comes into the middle. When I tie the hot in going either direction, I get 120v from neutral to ground. The Lights work. I know this should not be on the neutral or can this happen with fl lights. I've never had it before but I don't know that much about the internal working of ballasts.

Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#183026 - 12/22/08 12:43 PM Re: Florescent lights [Re: schenimann]
LarryC Offline

Registered: 07/05/04
Posts: 776
Loc: Winchester, NH, US
Sounds like a missing N-G bond at the source. Do these lights come off of new transformer? If so, I suspect a missing bond.

Larry C

#183027 - 12/22/08 12:56 PM Re: Florescent lights [Re: LarryC]
macmikeman Offline

Registered: 07/16/02
Posts: 718
Loc: Honolulu, Hawaii
I bet the neutral is not continous to the neutral busbar. Start checking at the branch source first and then out to the lights. Open circuit someplace.