#182807 - 12/12/08 05:47 AM Location of Disconneting means of sub panel
sokoservices Offline
Member
Registered: 01/10/08
Posts: 22
Loc: Virginia
Can someone help me out and find in the the NEC2005 where it talks about the location of a disconnect for a sub panel.

Its my unerstaning that you must have not more then 6 disconnecting means for a panel. Does this apply to a sub panel? If so its my undertanding its best to back feed the panel with a breaker and label that as the disconnecting means. OR you can install a fused dissconnect as long as it is "with in sight". Either way the disconneting means must be "with in sight".

I have found the following code referances:230.71 max number of disconnects, and also 230.91 location of OCD. Would these be the correct referances for my situation?

Thannk you as always

E
_________________________
Virginia Journeyman Eletrician
NFPA-70E Trained
CFC Universal Certified
Top
2017 / 2014 NEC & Related Books and Study Guides
#182809 - 12/12/08 07:09 AM Re: Location of Disconneting means of sub panel [Re: sokoservices]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6776
Loc: Brick, NJ USA
The 'disconnect' for a sub panel is the circuit breaker/fuses at the source of the feeder for said sub panel.

You must not exceed six (6) switches at the service entrance (excluding exemptions)
ie: a 'main' panel with six (6) switches/brkrs for the feeders/circuits sourced within that panel.

Yes, you can have a 'main' within (or adjacent) to the sub panel, but it is not required.
_________________________
John
Top
#182810 - 12/12/08 07:48 AM Re: Location of Disconneting means of sub panel [Re: HotLine1]
sokoservices Offline
Member
Registered: 01/10/08
Posts: 22
Loc: Virginia
As long as the feeding panel, with the CB, it is with in sight that makes sence. But if the feeding panel is not with in sight. I think you must have a CB on the feeders feeding the sub panel.


E
_________________________
Virginia Journeyman Eletrician
NFPA-70E Trained
CFC Universal Certified
Top
#182811 - 12/12/08 08:36 AM Re: Location of Disconneting means of sub panel [Re: sokoservices]
electure Offline


Member
Registered: 12/24/00
Posts: 4259
Loc: Fullerton, CA USA
HotLine1's right

There is no such requirement.

The only things that require a disconnect to be "in sight from " are transformers, motors, fixed heating equipment, storage batteries, tents and concessions, mobile homes, signs, and fixed appliances


Top
#182813 - 12/12/08 09:20 AM Re: Location of Disconneting means of sub panel [Re: electure]
sparky Offline
Member
Registered: 10/18/00
Posts: 5303
i don't recall a definition of subpanel, methinks that's our own jargon.

that aside, there's much ado about where said 'subpanel' may be.

for instance a 'subpanel' can be withing the same structure, or in a satelitte structure

this becomes, imho, the point of definitional confusion

in the latter case,iirc, although it may be referred to as 'the barn subpanel' it will still fall under the auspices of the 'service entrance' doctrine within the nec...

~S~
Top
#182817 - 12/12/08 11:25 AM Re: Location of Disconneting means of sub panel [Re: sparky]
sokoservices Offline
Member
Registered: 01/10/08
Posts: 22
Loc: Virginia
Originally Posted By sparky
i don't recall a definition of subpanel, methinks that's our own jargon.

that aside, there's much ado about where said 'subpanel' may be.

for instance a 'subpanel' can be withing the same structure, or in a satelitte structure

this becomes, imho, the point of definitional confusion

in the latter case,iirc, although it may be referred to as 'the barn subpanel' it will still fall under the auspices of the 'service entrance' doctrine within the nec...

~S~


So it is correct to say, it must have a single or no more then 6 means of disconnect in it. Or it must have a breaker back feeding the panel for a main.

E
_________________________
Virginia Journeyman Eletrician
NFPA-70E Trained
CFC Universal Certified
Top
#182818 - 12/12/08 12:00 PM Re: Location of Disconneting means of sub panel [Re: sokoservices]
gfretwell Online   content


Member
Registered: 07/20/04
Posts: 9038
Loc: Estero,Fl,usa
If the load side panel is in the same structure it does NOT need a local disconnect. If it is in a separate structure there does need to be a disconnecting means in that second building. The 6 throw rule really only applies to "power panelboards". "Lighting and appliance panelboards" (more than 10% of breakers serving branch circuits) can have no more than 2 main breakers. 408.16(A)
_________________________
Greg Fretwell
Top
#182820 - 12/12/08 02:13 PM Re: Location of Disconneting means of sub panel [Re: gfretwell]
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
Originally Posted By gfretwell
If the load side panel is in the same structure it does NOT need a local disconnect. If it is in a separate structure there does need to be a disconnecting means in that second building. The 6 throw rule really only applies to "power panelboards". "Lighting and appliance panelboards" (more than 10% of breakers serving branch circuits) can have no more than 2 main breakers. 408.16(A)

Greg- look at 225.32 & 225.33
_________________________
George Little
Top
#182822 - 12/12/08 02:42 PM Re: Location of Disconneting means of sub panel [Re: George Little]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6776
Loc: Brick, NJ USA
Hang on there guys...
The OP didn't say anything re: locations, multi-bldgs, etc.

Soko:
A little more detail/info please!!



_________________________
John
Top
#182824 - 12/12/08 03:06 PM Re: Location of Disconneting means of sub panel [Re: HotLine1]
WireNuts29 Offline
Member
Registered: 07/24/07
Posts: 85
Loc: Mass, U.S.A.
unless you're tapping into a set of larger ampacity wires,or bus duct, your sub panel, won't require a breaker. The feeders will be protected by the breaker which feeds them.
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 07/05/02
Posts: 8211
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 124 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals