#182786 - 12/10/08 11:54 AM Server Room Ground Bar
cgw Offline
Member
Registered: 07/29/04
Posts: 133
Loc: Rochester NY
Owner wants a ground bar in a small server room for bonding racks etc. Fairly typical. I will research it but can you give me a head start by letting me know what is typically done?
Bus bar size?
Bonding wire size? (size based on grounding electrode conductor, circuits serving the room, other?)
Where to bond to bldg ground?


Edited by cgw (12/10/08 11:56 AM)
Top
Work Gear for Electricians and the Trades
#182787 - 12/10/08 12:37 PM Re: Server Room Ground Bar [Re: cgw]
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5316
Loc: Blue Collar Country
The grounding bussbars I've seen have typically been HUGE ... perhaps 1" wide and 3/16" thick, simple copper.

While you don't need this much copper for a ground path, you do need that much for mechanical strength, and for the screws to have a couple threads engage the metal.

Hint: When drilling copper, you want to use drill bits with 135 degree 'split point' tips. When tapping, taps with spiral flutes work better. It's worth a visit to a local machine-shop supply house.
Top
#182793 - 12/10/08 09:38 PM Re: Server Room Ground Bar [Re: renosteinke]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9036
Loc: Estero,Fl,usa
Usually somebody in their tech staff will want a isolated ground conductor going straight to the equipment bonding bus in the service where the GEC and MBJ land. That might also serve a sub panel for the server room so all the circuits will share the same grounding path.
I think anything beyond standard 250 is usually snake oil. It is good to have a common grounding bus but where the ground comes from is not as important as getting all the equipment in the room bonded to that bus.


The ground bus plates an my radio equipment shelters were more like 4" x 16" and had a bunch of 1/4-20 tapped holes with brass screws in them already. They usually used a #4 cu solid to the ground electrode system, landing in the service disconnect can.
_________________________
Greg Fretwell
Top
#182801 - 12/11/08 12:05 PM Re: Server Room Ground Bar [Re: gfretwell]
SteveFehr Offline
Member
Registered: 03/19/05
Posts: 1195
Loc: Chesapeake, VA
There are a number of ways to do it. Often, I'll see nice thick ground bars under the false floor, way oversized, with big lugs from all the racks. He's concerned about higher frequency ground currents, so the properties are very different than for 60Hz safety grounds. For instance, a metal raised deck that's insulated and not even touching the ground will have lower impedance to ground than a 20' ground rod, because the capacitance between the false floor and ground is essentially a short at higher frequencies, wheras the ground wire and rod function as a 0-loop inductor and have a high impedance.

Google MIL-HDBK-1012/1, it's a miliary handbook dealing with datacenters. It's free, and a good design reference smile MIL-HDBK-419 also deals with grounding. You can ignore TEMPEST (security) and HEMP (nuclear) requirements.
Top
#182804 - 12/11/08 03:17 PM Re: Server Room Ground Bar [Re: gfretwell]
TOOL_5150 Offline
Member
Registered: 08/01/07
Posts: 61
Loc: Bay Area
Originally Posted By gfretwell
The ground bus plates an my radio equipment shelters were more like 4" x 16" and had a bunch of 1/4-20 tapped holes with brass screws in them already. They usually used a #4 cu solid to the ground electrode system, landing in the service disconnect can.


This is usually what I saw when I worked on the big nortel meridian phone systems as well.

~Matt
_________________________
I would rather beg for forgiveness then beg for permission.
Top
#183170 - 12/28/08 07:59 PM Re: Server Room Ground Bar [Re: TOOL_5150]
Steve Miller Offline
Member
Registered: 08/30/01
Posts: 325
Loc: Loudoun Cty, VA
All of our new schools have exactly what gfretwell describes (in the server room). 4x16 by 1/4" thick with a lot of threaded holes. A #4 to the main electrical room via a pipe below the slab. Every piece of eqpt has an 8 or 6 to this plate. Seems to work well. We've been using this system for about 6 or 8 years now and have very few probs.
Top
#183172 - 12/28/08 08:31 PM Re: Server Room Ground Bar [Re: Steve Miller]
leland Offline
Member
Registered: 08/20/07
Posts: 853
Loc: Lowell area, Ma. USA
Thats the same I see all the time,additionaly they are all on raised Isolators.
Top
#183552 - 01/13/09 08:05 PM Re: Server Room Ground Bar [Re: leland]
noderaser Offline
Member
Registered: 03/01/07
Posts: 404
Loc: Portland, Oregon, United State...
Here's the ground bar in one of our switch closets, for reference:

_________________________
http://www.hsiprodsvcs.com/
Top
#183695 - 01/19/09 01:54 PM Re: Server Room Ground Bar [Re: noderaser]
Brian_John Offline
New Member
Registered: 05/14/07
Posts: 7
Loc: Leesburg, VA
In our area you can get a 1/4" X 12" (or 24") X4" from the local sheet metal fabricator. These ground bars in the typical server room do little the expend natural resources and make the end user feel good (oh and it adds profits to the installing electrical contractors pockets always a bonus)
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 61 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals