#182745 - 12/08/08 05:02 PM m-h wall pack
Sandro Offline
Member
Registered: 12/30/01
Posts: 444
Loc: Stoney Creek, ON, Canada
Replaced a wall light with a brand new 400w metal halide wall pack on an old hotel for a customer.

Upon energizing to test it, the lamp would not light. While trouble shooting, it turns out that when only the ground wire was disconnected, the lamp would light. Of course, when the ground was connected, the bulb would go out.

Any ideas?
Top
Work Gear for Electricians and the Trades
#182749 - 12/08/08 06:14 PM Re: m-h wall pack [Re: Sandro]
walrus Offline
Member
Registered: 07/25/02
Posts: 680
Loc: Bangor Me. USA
Bad ballast? seems like the only thing in there that would be grounded
Top
#182750 - 12/08/08 06:48 PM Re: m-h wall pack [Re: walrus]
frenchelectrican Offline
Member
Registered: 02/06/03
Posts: 939
Loc: Wi/ Paris France { France for ...
What voltage this luminaire is wired up for ? I have a hunch it may have wrong ballast to use in there.

Merci.

Marc
_________________________
Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)

Top
#182788 - 12/10/08 04:51 PM Re: m-h wall pack [Re: frenchelectrican]
Sandro Offline
Member
Registered: 12/30/01
Posts: 444
Loc: Stoney Creek, ON, Canada
Originally Posted By frenchelectrican
What voltage this luminaire is wired up for ? I have a hunch it may have wrong ballast to use in there.

Merci.

Marc



It's a tri-tap ballast. The proper 120V lead is connected, the other two leads are factory sealed and unexposed.

The fixture is brand new, complete with lamp and ballast. I have used many of this same type of fixture without any problem.

I take it nobody else has encountered this type of problem before.




Top
#182794 - 12/10/08 09:48 PM Re: m-h wall pack [Re: Sandro]
Rewired Offline
Member
Registered: 01/01/06
Posts: 558
Loc: Hamilton, Ontario, Canada
Is the capacitor in the fixture metallic by chance?? I would start looking at something between the ballast output lead (if not the ballast itself) and the socket accidentally touching ground or faulted to ground, and my first bet would be a capacitor with a metallic case and an internal problem ..


A.D
Top

Member Spotlight
Member Since: 07/05/02
Posts: 8211
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 124 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals