#182578 - 12/02/08 09:26 PM motor starter
Sandro Offline
Member
Registered: 12/30/01
Posts: 444
Loc: Stoney Creek, ON, Canada
Ever get those jobs where you think you "know" something can be done, but due to brain cramp, can't figure it out??

With a push button motor starter (1 stop, 1 start. Not a manual button starter but one controlled with coil), connected to a compressor with pressure switch. When the pressure switch opens the circuit and breaks the coil contact, it takes the operator to push the start button again once the pressure drops to get the motor going again.

Argh! the holding contact, I believe there is a way around this..... and can't quite remember how to do this. Wire the pressure switch into the aux contacts?
Top
Work Gear for Electricians and the Trades
#182579 - 12/02/08 09:31 PM Re: motor starter [Re: Sandro]
twh Offline
Member
Registered: 03/11/04
Posts: 901
Loc: Regina, Sask.
I think a compressor needs an off-auto switch.


Edited by twh (12/02/08 09:34 PM)
Edit Reason: changed switch type
Top
#182580 - 12/02/08 09:45 PM Re: motor starter [Re: twh]
wire_twister Offline
Member
Registered: 07/25/07
Posts: 265
Loc: Georgia USA
You need an off-auto switch, or a locking run push button
_________________________
Jimmy

Life is tough, Life is tougher when you are stupid
Top
#182581 - 12/02/08 10:31 PM Re: motor starter [Re: wire_twister]
JoeTestingEngr Offline
Member
Registered: 11/04/05
Posts: 781
Loc: Chicago, Il.
I don't think I would leave it that way. I would fill the holes with a press-to-test indicator and a momentary-off-on rotary selector switch. The pressure switch should have a pressure and deadband or differential adjustment. The Off position breaks path to N.C. opens on P increase, switch terminals. The momentary, "Hand" position, parallels P-switch, to check operation without bleeding the tank. The N.O. aux switch would be used to drive your indicator. Do you have any E-stops in the mix? You wouldn't need any holding contacts unless you were going to use 2 separate pressure switches in series. In that case, the holding contact is in parallel with the low pressure switch. It helps to think of one as "closes on low pressure", and the other as, "opens on high pressure"
Joe
Top
#182582 - 12/02/08 10:58 PM Re: motor starter [Re: JoeTestingEngr]
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5316
Loc: Blue Collar Country
Seems like someone is trying to defeat a safety device ... to me. If there's a high-pressure cut off switch, it's there for a reason. I'm not about to give advice on defeating it.

If you want the compressor to automatically re-start when the pressure has dropped ... well, that's a normal control problem, and would be solved by adding a pressure switch - not by bypassing an existing one.

I'm real close to locking this thread. Did I understand the request correctly?
Top
#182583 - 12/03/08 12:59 AM Re: motor starter [Re: renosteinke]
gfretwell Online   content


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
I didn't read this as an over pressure switch, just the one that establishes proper tank pressure.
_________________________
Greg Fretwell
Top
#182584 - 12/03/08 06:09 AM Re: motor starter [Re: gfretwell]
Sandro Offline
Member
Registered: 12/30/01
Posts: 444
Loc: Stoney Creek, ON, Canada
BINGO!!!
Top
#182585 - 12/03/08 06:10 AM Re: motor starter [Re: gfretwell]
Sandro Offline
Member
Registered: 12/30/01
Posts: 444
Loc: Stoney Creek, ON, Canada
Originally Posted By gfretwell
I didn't read this as an over pressure switch, just the one that establishes proper tank pressure.


BINGO!
Top
#182589 - 12/03/08 09:35 AM Re: motor starter [Re: Sandro]
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5316
Loc: Blue Collar Country
Thanks for the clarification.
Top
#182590 - 12/03/08 10:27 AM Re: motor starter [Re: renosteinke]
electure Offline


Member
Registered: 12/24/00
Posts: 4259
Loc: Fullerton, CA USA
Quote:
Argh! the holding contact, I believe there is a way around this.....


Forget the holding contact

You need to bypass the holding contact entirely, and run the coil directly from the pressure differential switch.

A MAINTAINED contact switch can be inserted anywhere in the control circuit to turn it off.


Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 04/03/02
Posts: 6778
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 70 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals