The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
230 or 345 kV transmission lines?
by Vlado
Yesterday at 09:33 AM
breaker meltdown
by crselectric
Yesterday at 12:42 AM
Electrical mast flashing product
by ThomasWinfrey
09/22/16 12:14 AM
What estimating software do you recommend?
by sparky
09/21/16 07:20 PM
"Dry Run" Inspection goes awry
by HotLine1
09/20/16 07:39 PM
New in the Gallery:
12.5A through 0.75mm flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 15
sparky 9
gfretwell 8
sparky66wv 8
Vlado 6
Who's Online
0 registered (), 258 Guests and 6 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#182286 - 11/23/08 10:03 AM MWBC with 2 out of 3 phases
walrus Offline
Member

Registered: 07/25/02
Posts: 671
Loc: Bangor Me. USA
I saw this on a lighting circuit. A 2 pole breaker, in a 3 phase panel, feeding 2 120v circuits sharing one neutral. Knew the neutral wouldn't be 0 and it wasn't, it was less than either hot though. Anything wrong with this practice?

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#182288 - 11/23/08 11:37 AM Re: MWBC with 2 out of 3 phases [Re: walrus]
renosteinke Offline
Cat Servant
Member

Registered: 01/22/05
Posts: 5299
Loc: Blue Collar Country
Nothing wrong with that at all. The remaining voltage is the direct result of the two legs not being 180 degrees out of time with each other.

Top
#182303 - 11/23/08 01:42 PM Re: MWBC with 2 out of 3 phases [Re: renosteinke]
Texas_Ranger Offline
Member

Registered: 12/17/01
Posts: 2331
Loc: Vienna, Austria
In this case the neutral sees the geometric sum of the current in both phases. If only one phase of a 3 phase system were loaded the neutral would see the full phase current.

Top
#182322 - 11/23/08 06:05 PM Re: MWBC with 2 out of 3 phases [Re: Texas_Ranger]
frenchelectrican Offline

Member

Registered: 02/06/03
Posts: 938
Loc: Wi/ Paris France { France for ...
A simple rule anytime you run 1 off from 3 WYE system is that you have to have netural conductor the same size as phase conductor.

I don't excatally recall how I did that forumla it was a while seice I done that but corret me if I am wrong.,

( L1-L2 ) / N * 30

I am not sure if that work right due the phase shift affect on it.

A true single phase MWBC will cancel netural current due 180 shift as long L1 - L2 load is the same the netrual current will read zero { not excactally but it will show near 0 on it }

Merci,Marc
_________________________
Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)


Top
#182346 - 11/24/08 05:44 AM Re: MWBC with 2 out of 3 phases [Re: frenchelectrican]
Ichabod Offline
Member

Registered: 05/24/03
Posts: 26
Loc: Statesboro, GA, USA
Think of it this way: assume you have a balanced 3 phase wye load and the currents are 10 amps at 0 degrees, 120 degrees, and 240 degrees. Add the 10 amps at 0 and 120 degrees and you get 10 amps at 60 degrees, which is 180 degrees from the 240 degree load and that adds to 0 amps in the neutral. So the highest load on the neutral can not be higher than any of the phases. Nothing wrong with a shared neutral circuit.

Ichabod

Top
#182348 - 11/24/08 05:54 AM Re: MWBC with 2 out of 3 phases [Re: Ichabod]
SteveFehr Offline
Member

Registered: 03/19/05
Posts: 1192
Loc: Chesapeake, VA
A neutral like this will have less current than if it was a single phase off the 3-phase panel, but typically more than if it was in a residential 120/240. It's normal and OK, and will never exceed 100% ampacity. Well, not in normal circuimstances, at least...

Top
#182385 - 11/24/08 11:33 PM Re: MWBC with 2 out of 3 phases [Re: SteveFehr]
pdh Offline
Member

Registered: 01/20/05
Posts: 354
Originally Posted By: SteveFehr
It's normal and OK, and will never exceed 100% ampacity. Well, not in normal circuimstances, at least...

One abnormal circumstance is low pf, leading on one phase and lagging on the other. mad

Top
#182391 - 11/25/08 05:36 AM Re: MWBC with 2 out of 3 phases [Re: pdh]
SteveFehr Offline
Member

Registered: 03/19/05
Posts: 1192
Loc: Chesapeake, VA
Originally Posted By: pdh
One abnormal circumstance is low pf, leading on one phase and lagging on the other. mad
I must say, that's a new one! I was more referring to 3-phase 6-step power supplies, but I can your PF problem being especially bad on a circuit with two 208V legs. There's an easy solution, though: swap the legs if that occurs, and the currents cancel, problem solved!

Top
#182409 - 11/25/08 01:46 PM Re: MWBC with 2 out of 3 phases [Re: SteveFehr]
pdh Offline
Member

Registered: 01/20/05
Posts: 354
Originally Posted By: SteveFehr
Originally Posted By: pdh
One abnormal circumstance is low pf, leading on one phase and lagging on the other. mad
I must say, that's a new one! I was more referring to 3-phase 6-step power supplies, but I can your PF problem being especially bad on a circuit with two 208V legs. There's an easy solution, though: swap the legs if that occurs, and the currents cancel, problem solved!

But if the pf is very low, you are only reducing the problem, not eliminating it. And this one can be bad in those extreme cases with 180 degree legs at 120/240V. Fortunately, such cases are unheard of in residential situations.

Top
#182492 - 11/28/08 05:30 PM Re: MWBC with 2 out of 3 phases [Re: pdh]
Texas_Ranger Offline
Member

Registered: 12/17/01
Posts: 2331
Loc: Vienna, Austria
In Europe larger companies are having all sorts of trouble with large numbers of switching mode power supplies on 3 phase supplies which can raise the neutral current above that of the largest phase current.