The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Temporarily feeding a panel...
by HotLine1
Today at 07:07 PM
Locked rotor, no burnout
by jraef
Today at 01:18 PM
Massive power outage South Australia
by Meadow
Today at 06:46 AM
short circuit??
by Meadow
Today at 06:43 AM
Norwegian power?
by Meadow
Today at 06:36 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 14
sparky 10
gfretwell 8
sparky66wv 8
Vlado 6
Who's Online
0 registered (), 276 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#182185 - 11/20/08 01:22 PM Does 310.15 overrule temperature limitations?
Mills Offline
New Member

Registered: 09/24/04
Posts: 6
Loc: Carolina
I can't seem to reconcile T 310.15(B)(6) with 110.14(C)(1)(b)(1). What do you think?

This is a residential single phase overhead service drop, going to a GE meter center with feed thru lugs. The 200A main will protect the feeder to a 200A subpanel inside. Local jurisdiction using 2005 NEC.

Does 2005 NEC T310.15(B)(6) allow 4/0 Al for service and feeder, or is that trumped by the manufacturer’s label [Use 60/75C conductors], which would require 250 kcmil?

Thanks,
Mills

Top
2014 / 2011 NEC & Related Books and Study Guides
#182187 - 11/20/08 02:04 PM Re: Does 310.15 overrule temperature limitations? [Re: Mills]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9012
Loc: Estero,Fl,usa
Two different things.
310.15(B)(6) gives you a break on the ampacity because they know there is a lot of diversity in the total load of a dwelling. You are not using 310.16 at all.
_________________________
Greg Fretwell

Top
#182221 - 11/21/08 06:25 AM Re: Does 310.15 overrule temperature limitations? [Re: Mills]
SteveFehr Offline
Member

Registered: 03/19/05
Posts: 1192
Loc: Chesapeake, VA
Originally Posted By: Mills
Does 2005 NEC T310.15(B)(6) allow 4/0 Al for service and feeder, or is that trumped by the manufacturer’s label [Use 60/75C conductors], which would require 250 kcmil?
The safe bet is always to ask your AHJ as theirs is the only opinion that matters, but I concur with Greg, 310.15(B)(6) requires 4/0, and specifically states you don't have to go larger. 310.16 does not apply to this cable.