#182028 - 11/16/08 09:45 AM Bonding at the HMBT
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
Where do you terminate the #8 bonding wire used around the Hydro-Massage Bath Tub (HMBT) if the water circulating pump is double insulated and has no bonding lug on it? I sent in a proposal to terminate it in the J-box of the branch circuit supplying the tub motor.
_________________________
George Little
Top
2017 / 2014 NEC & Related Books and Study Guides
#182032 - 11/16/08 10:56 AM Re: Bonding at the HMBT [Re: George Little]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
They may say that the intent of equipotential bonding does not include tying it to the EGC pointing to the FPN in 680.26(A) but it is not a bad idea. I agree that in a double insulated all plastic installation there is not much to bond. At a certain point I would be asking about the floor. Is it concrete with tile? That may be the next thing to look at if you want to worry about something. That is yet another selling point for the Ufer and bonding the wire in the floor to the rebar in the footer.
_________________________
Greg Fretwell
Top
#182152 - 11/19/08 04:52 PM Re: Bonding at the HMBT [Re: gfretwell]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6778
Loc: Brick, NJ USA
George:
Did I not read somewhere words to the effect that 'if there is nothing to bond; you're done'??

Double insul motor and PEX piping?
Normal motor with lug, PEX piping (or other brand plastic) with PVC waste??

Going to the panel can create a parallel ground path, con it not?

_________________________
John
Top
#182160 - 11/19/08 06:56 PM Re: Bonding at the HMBT [Re: HotLine1]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
What's wrong with parallel grounding paths, we do it all the time, in fact in health care it is required.
In your typical pool installation you have several parallel ground paths. EGC in the underwater light is connected to the bonding grid, as is the case of the pool pump, the cover motor, the heater and any electrical equipment mounted to the screen cage.
_________________________
Greg Fretwell
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6778
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 63 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals