The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
failed home inspection.
by HotLine1
17 minutes 20 seconds ago
Safety at heights?
by Trumpy
Today at 05:25 AM
Old Bath Fan
by gfretwell
Today at 01:38 AM
Search Function
by Webmaster
Yesterday at 11:13 PM
Forum Software Upgrade coming soon...
by Webmaster
Yesterday at 09:17 PM
New in the Gallery:
Desk-mounted "power-board"
Top Posters (30 Days)
Webmaster 30
HotLine1 21
Ruben Rocha 16
Trumpy 13
gfretwell 13
Who's Online
2 registered (HotLine1, Webmaster), 0 Guests and 195 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#182028 - 11/16/08 09:45 AM Bonding at the HMBT
George Little Offline
Member

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
Where do you terminate the #8 bonding wire used around the Hydro-Massage Bath Tub (HMBT) if the water circulating pump is double insulated and has no bonding lug on it? I sent in a proposal to terminate it in the J-box of the branch circuit supplying the tub motor.
_________________________
George Little

Top
2017 / 2014 NEC & Related Books and Study Guides
#182032 - 11/16/08 10:56 AM Re: Bonding at the HMBT [Re: George Little]
gfretwell Offline


Member

Registered: 07/20/04
Posts: 9063
Loc: Estero,Fl,usa
They may say that the intent of equipotential bonding does not include tying it to the EGC pointing to the FPN in 680.26(A) but it is not a bad idea. I agree that in a double insulated all plastic installation there is not much to bond. At a certain point I would be asking about the floor. Is it concrete with tile? That may be the next thing to look at if you want to worry about something. That is yet another selling point for the Ufer and bonding the wire in the floor to the rebar in the footer.
_________________________
Greg Fretwell

Top
#182152 - 11/19/08 04:52 PM Re: Bonding at the HMBT [Re: gfretwell]
HotLine1 Online   content


Member

Registered: 04/03/02
Posts: 6832
Loc: Brick, NJ USA
George:
Did I not read somewhere words to the effect that 'if there is nothing to bond; you're done'??

Double insul motor and PEX piping?
Normal motor with lug, PEX piping (or other brand plastic) with PVC waste??

Going to the panel can create a parallel ground path, con it not?

_________________________
John

Top
#182160 - 11/19/08 06:56 PM Re: Bonding at the HMBT [Re: HotLine1]
gfretwell Offline


Member

Registered: 07/20/04
Posts: 9063
Loc: Estero,Fl,usa
What's wrong with parallel grounding paths, we do it all the time, in fact in health care it is required.
In your typical pool installation you have several parallel ground paths. EGC in the underwater light is connected to the bonding grid, as is the case of the pool pump, the cover motor, the heater and any electrical equipment mounted to the screen cage.
_________________________
Greg Fretwell

Top