#182004 - 11/14/08 09:02 PM Temporary Power Pole Question
davemica Offline
Member
Registered: 10/26/05
Posts: 12
Loc: florida
Does the NEC require a 20A-240V receptacle (for an air compressor) to be protected by a gfi on a temporary power pole.
Top
2017 / 2014 NEC & Related Books and Study Guides
#182007 - 11/15/08 08:58 AM Re: Temporary Power Pole Question [Re: davemica]
electure Offline


Member
Registered: 12/24/00
Posts: 4259
Loc: Fullerton, CA USA
No.
See 590.6 (A) Temporary Installations

"Receptacle Outlets. All 125-volt, single-phase, 15-,20-, and 30-ampere receptacle outlets that are not a part of the permanent wiring of the building or structure and that are in use by personnel shall have ground-fault circuit interrupter protection for personnel."

240 volt receptacles are exempt

Top
#182013 - 11/15/08 06:19 PM Re: Temporary Power Pole Question [Re: electure]
caselec Offline
Member
Registered: 04/14/02
Posts: 558
Loc: San Jose, CA
If you don't provide GFCI protection you must have a Assured Equipment Grounding Conductor Program.
_________________________
Curt Swartz
Top

Member Spotlight
Member Since: 07/05/02
Posts: 8211
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 124 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals