#181965 - 11/12/08 06:38 PM Motor feeder voltage drop
cgw Offline
Member
Registered: 07/29/04
Posts: 133
Loc: Rochester NY
When the elevator manufacturer says to not exceed 3% drop in the voltage do they mean at motor start or at the running current?
Top
Work Gear for Electricians and the Trades
#181970 - 11/12/08 11:43 PM Re: Motor feeder voltage drop [Re: cgw]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
Based on FLA of the total motor load plus 25% of the largest motor, would be my guess.
_________________________
Greg Fretwell
Top
#182038 - 11/16/08 11:35 AM Re: Motor feeder voltage drop [Re: gfretwell]
JValdes Offline
Member
Registered: 06/03/07
Posts: 301
Loc: South Carolina
Running. You would never meet 3% VD on start.
Top