#181825 - 11/02/08 08:24 AM annondized copper
watersparkfalls Offline
Member
Registered: 03/08/05
Posts: 212
Loc: Washington...Not DC
Is annondized copper properties the same as copper?
I only ask because a friend pulled an additional set of parralell feeders before they realized that the existing sets of feeders were(they thouht alum at first)annondized copper. Since parralell runs are important to be exact(length,insulation,metal ect...)to insure current flows through each conductor evenly to avoid overheating on them.

thanks,
H20
Top
2017 / 2014 NEC & Related Books and Study Guides
#181831 - 11/02/08 11:27 AM Re: annondized copper [Re: watersparkfalls]
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5316
Loc: Blue Collar Country
Aluminum is anodized; copper is not. Aluminum wire is never anodized - that would be a high resistance connection, but it might be copper coated.

Copper wire MIGHT have tinned condustors; these will have a silvery appearance.

I would treat tinned copper the same as plain copper.
Top
#181844 - 11/03/08 08:59 AM Re: annondized copper [Re: renosteinke]
mikesh Offline
Member
Registered: 06/07/06
Posts: 613
Loc: Victoria, BC, Canada
Anode (izing) is the electric fusion of aluminum oxide to aluminum to protect against uncontroled aluminum oxidization and because the anodizing is also harder than the underlying aluminum it also protects the part from wear too. It can be dyed too. Anodizing increases electrical resistance and is not used in wire.
The electrical process dips an aluminu part in an acid solution with suspended aluminum oxide in the solution. the part is connected as the anode and the tank as the cathode. and electricity causes the oxide to deposit on the aluminum. Electroplating is done in a similar manner.
Top
#181860 - 11/04/08 03:08 PM Re: annondized copper [Re: mikesh]
Tom Offline
Member
Registered: 01/01/01
Posts: 1044
Loc: Shinnston, WV USA
If that feeder is really old, it could be tin plated copper. The tin plating was put on to prevent a reaction between the copper and the rubber insulation. Though usualy silver in appearance, sI've seen it look slightly yellow or gold.


Edited by Tom (11/04/08 03:09 PM)
_________________________
Few things are harder to put up with than the annoyance of a good example.
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 42 Guests and 11 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals