#181746 - 10/28/08 10:54 AM Service size for spec office space
cgw Offline
Member
Registered: 07/29/04
Posts: 133
Loc: Rochester NY
I'm trying to estimate a service size for a samll office building. My estimate works out to 10W/SF. Previous projects are all around 10W/SF. It is for a 14,800 square foot building for which I have preliminary floor plans for a small part of it (two tenents). 12 W/SF sound right? There is an elevator which I will add on top (of the 12W/SF) along with other house loads like exterior lighting.
Top
Work Gear for Electricians and the Trades
#181748 - 10/28/08 01:14 PM Re: Service size for spec office space [Re: cgw]
wa2ise Offline
Member
Registered: 11/29/02
Posts: 782
Loc: Oradell NJ USA
I imagine that much of that load will be computers and such with really bad power factors and drawing current with lots of harmonics. Which means you'd need individual neutrals or superneutrals to handle it.
Top
#181749 - 10/28/08 02:08 PM Re: Service size for spec office space [Re: wa2ise]
ghost307 Offline
Member
Registered: 05/09/05
Posts: 900
Loc: Chicago Illinois USA
Make sure that the HVAC loads aren't coming out of your 12 W/SF. They can eat up a lot of power quickly.
_________________________
Ghost307
Top
#181752 - 10/28/08 07:11 PM Re: Service size for spec office space [Re: ghost307]
cgw Offline
Member
Registered: 07/29/04
Posts: 133
Loc: Rochester NY
The HVAC is included.
By NEC lighting is 3.5W/SF and receptacles 1W/SF (off the top of my head). In practice receptacle loads are higher (at least 2W/SF). Lighting will be less than 2W/SF but (as far as I can tell) we need to use the 3.5.
Electric for HVAC is fairly predictable.
Top

Member Spotlight
Member Since: 07/05/02
Posts: 8211
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 55 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals