The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
Today at 04:24 PM
On Delay Relay with Auto Reset
by Potseal
Yesterday at 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Texas_Ranger 8
Trumpy 8
sparkyinak 7
Who's Online
0 registered (), 202 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 3 1 2 3 >
Topic Options
Rate This Topic
#18174 - 12/06/02 07:17 PM please advise: compressor keeps tripping breaker
INTP Offline
Member

Registered: 09/10/02
Posts: 14
Loc: Dallas, Tx, USA
My craftsman 5.5HP air compressor keeps tripping the breaker when it cycles on. not every time, but 1 out of 3 or so. If it doesn't trip when it kicks on, it will be ok until the beginning of the next cycle.

It's on a 20A 115V circuit by itself. The 12GA run to the sub panel is only about 20' of wire. I've tried a different breaker, and it does the same thing. It's a tandem (two breakers on one 115V pole), but it did it with a regular breaker, too. The subpanel is Square D homeline. Nothing else gives me any problems, either at the subpanel or the main. I've even run my MIG welder off the same receptacle (not at the same time) and it didn't trip it.

Any suggestions?

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#18175 - 12/06/02 07:28 PM Re: please advise: compressor keeps tripping breaker
Wirenuttt Offline
Member

Registered: 11/10/02
Posts: 267
Loc: Massachusetts
Check the nameplate for fla (full load amps) You may have to run a larger line and a larger circuit breaker. 5.5hp is 4103 watts at over 30 amps. Not sure if that motor actually uses that, so check the name plate and size accordingly. Hope this helps.

Top
#18176 - 12/06/02 07:28 PM Re: please advise: compressor keeps tripping breaker
electure Offline

Member

Registered: 12/24/00
Posts: 4226
Loc: Fullerton, CA USA
Probably time to call an electrician!

[This message has been edited by electure (edited 12-06-2002).]

Top
#18177 - 12/06/02 08:21 PM Re: please advise: compressor keeps tripping breaker
INTP Offline
Member

Registered: 09/10/02
Posts: 14
Loc: Dallas, Tx, USA
Thanks, wirenut. I can't find the FLA anywhere. It just says 115V/60Hz/1PH/15A. Max developed HP=6. Lots of stuff about flow (cfm).

The voltage at the receptacle is 123.5, FWIW.

Top
#18178 - 12/06/02 08:36 PM Re: please advise: compressor keeps tripping breaker
Bill Addiss Offline
Member

Registered: 10/07/00
Posts: 4196
Loc: NY, USA
You should call the Manufacturer and see if they are aware of any issues with this unit.

Bill

Top
#18179 - 12/06/02 08:52 PM Re: please advise: compressor keeps tripping breaker
electric-ed Offline
Member

Registered: 07/08/02
Posts: 184
Loc: Canada
With a 15 amp rating, this motor will draw a starting inrush current of 45 to 75 amps. It is not surprising that the 20 amp breaker trips. This motor is permitted a breaker rated at 250% of 15 amps.

2.5 X 15 = 37.5 amps. Try a 30 amp breaker.

Ed

[This message has been edited by electric-ed (edited 12-06-2002).]

Top
#18180 - 12/06/02 09:01 PM Re: please advise: compressor keeps tripping breaker
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
Does this problem occur when the storage tank is empty? If it only occurs when there is pressure in the tank, it sounds like the "unloading" valve is not functioning correctly. This valve dumps the air from the compressor cylinders when the motor stops turning and makes the starting load much less. If the motor tries to start with pressure in the cylinders, I would expect it to trip the breaker.
Don
_________________________
Don(resqcapt19)

Top
#18181 - 12/06/02 09:08 PM Re: please advise: compressor keeps tripping breaker
The Watt Doctor Offline
Member

Registered: 12/23/01
Posts: 443
Loc: Mont Belvieu, TX
If this compressor is "cord and plug" connected with an "OEM" cord, then it was designed to be "plugged in" to a receptacle. Maybe the bearings in the motor are about to fail, or the internal parts in the compressor are worn, and causing the motor to be overloaded. Are there any other loads on that circuit?

Decompressing,
Doc
_________________________
The Watt Doctor
Altura Cogen
Channelview, TX

Top
#18182 - 12/06/02 10:09 PM Re: please advise: compressor keeps tripping breaker
bobp Offline
Member

Registered: 10/14/02
Posts: 73
Loc: Puyallup, WA, USA
Is it a breaker or a GFI that's tripping. If it's a breaker then see electric ed above. If it's a GFI then plug it in on a non-GFI receptacle.

Bob

Top
#18183 - 12/06/02 11:36 PM Re: please advise: compressor keeps tripping breaker
Mike_Riverside Offline
Member

Registered: 08/18/02
Posts: 34
I used to have a Craftsman 5.5 HP compressor. The book says to put on dedicated 15A circut or a 20A circut. I ran it on a 15A circut and never once tripped the breaker.

The motor has a plastic box over it...so you cannont read the nameplate without taking off the cover.

(Removed long non-working url)

[This message has been edited by Webmaster (edited 12-07-2002).]