The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Forum Software Upgrade coming soon...
by Webmaster
42 minutes 17 seconds ago
Re: Fabricating Guards out of Lexan?
by frank
Today at 04:11 PM
Would ELV branch circuits be a good idea?
by gfretwell
Today at 01:26 PM
Why cables look like they do
by Texas_Ranger
Today at 12:33 PM
100% breakers?
by Texas_Ranger
Yesterday at 06:13 AM
New in the Gallery:
Desk-mounted "power-board"
Shout Box

Top Posters (30 Days)
HotLine1 20
Webmaster 16
Trumpy 12
ghost307 12
frank 11
Who's Online
1 registered (Webmaster), 0 Guests and 66 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#181554 - 10/15/08 07:54 PM Collector Bus sizing Problem
theseus Offline
Member

Registered: 02/23/08
Posts: 11
Loc: china
How to size the Collector Bus?
I have 3 1600kw/400V gengerators Synchronized and connected to the Collector Bus.

Top
#181567 - 10/16/08 08:52 AM Re: Collector Bus sizing Problem [Re: theseus]
mikesh Offline
Member

Registered: 06/07/06
Posts: 614
Loc: Victoria, BC, Canada
Ok I'll bite, (1600 X 125%) + 1600 + 1600 = 5200 amps.
28-108 of the Canadian Electrical code for conductor sizing for Motors.

Method 2 take the connected load at 125% and size the bus for that.

I don't know what a collector bus is but i guessed it is the bus after the transfer switches where each generator parallels.

Top
#181585 - 10/16/08 09:50 PM Re: Collector Bus sizing Problem [Re: mikesh]
theseus Offline
Member

Registered: 02/23/08
Posts: 11
Loc: china
Yes,Collector bus = paralleling bus.

But,generator is different from motor.

Top
#181620 - 10/20/08 09:46 AM Re: Collector Bus sizing Problem [Re: theseus]
mikesh Offline
Member

Registered: 06/07/06
Posts: 614
Loc: Victoria, BC, Canada
Yes a generator and a motor are not the same but the wires are sized the same. At least that is what i derive from section 28 of the CEC %125 of the first (largest) generator and 100% of the next 2. Generators and motors are very similar in terms of what happens inside them whether making or using electricity. Cooling, winding and loading all apply the same. A stator for a motor and a generator look the same from a winders perspective at least from 28 year old memories they do. I have rewound stators for both. The armatures are different as there is excitation and magnetic fields to build.