The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Live Chat Feature
by Admin
Yesterday at 09:52 PM
Safety at heights?
by gfretwell
Yesterday at 07:16 PM
failed home inspection.
by gfretwell
Yesterday at 07:03 PM
Webmaster > Admin
by Admin
Yesterday at 05:49 PM
Old Bath Fan
by gfretwell
Yesterday at 01:38 AM
New in the Gallery:
Desk-mounted "power-board"
Top Posters (30 Days)
Admin 33
HotLine1 21
Ruben Rocha 16
gfretwell 15
Trumpy 13
Who's Online
1 registered (gfretwell), 0 Guests and 170 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#181423 - 10/07/08 11:06 AM Redundant Ground MC
gunther Offline
Member

Registered: 09/17/03
Posts: 59
I haven't found any information about how to terminate the redundant ground wire that comes in the green mc that is suitable for patient care areas. One opinion was to fold it back over the mc and make sure the mc fitting clip caught it, another was to wrap it around the outside grooves of the mc and catch it with the clip, and another was to use land it under the bolt that tightens the clip.
My thought would be to just make it up with the regular ground in the device box.
Is there a detail on this proceedure that I am missing?

Top
2017 / 2014 NEC & Related Books and Study Guides
#181424 - 10/07/08 11:36 AM Re: Redundant Ground MC [Re: gunther]
electure Offline


Member

Registered: 12/24/00
Posts: 4229
Loc: Fullerton, CA USA
Just fold it back, and cut it off at the armor, if you're talking about Southwire's product.

http://www.southwire.com/processGetPage.do?bp=featuredProduct.jsp

Click on "view installation steps"




Top
#181426 - 10/07/08 01:30 PM Re: Redundant Ground MC [Re: electure]
gunther Offline
Member

Registered: 09/17/03
Posts: 59
Thanks, that helps a lot. Although the mc shown isn't the type suitable for patient care areas, with the insulated green ground and also the bare redundant ground that accompanies it, it does explain that the ground is sufficient because it is in contact throughout and evidently the fitting is sufficient for continuous ground purposes.
The only question I might have is that this type of mc is green in color and I wonder if it is a non-conductive paint. I appreciate your help.

Top
#181427 - 10/07/08 01:47 PM Re: Redundant Ground MC [Re: gunther]
gunther Offline
Member

Registered: 09/17/03
Posts: 59
Update: I just called the manufacturer and they say that it has been tested to perform excellently when the bare conductor is cut off where it comes out of the jacket.

Top
#181436 - 10/07/08 06:30 PM Re: Redundant Ground MC [Re: gunther]
SolarPowered Offline
Member

Registered: 07/05/04
Posts: 615
Loc: Palo Alto, CA, USA
Just FYI, I believe that the HCF cable is actually AC cable, not MC.

Top
#181437 - 10/07/08 07:11 PM Re: Redundant Ground MC [Re: SolarPowered]
electure Offline


Member

Registered: 12/24/00
Posts: 4229
Loc: Fullerton, CA USA
It's MC, a type that came out recently.

From the site linked to above:

"UL-listed and NEC-compliant MCAP and HCF MCAP can replace conventional AC or MC cable in a broad range of applications."


Edited by electure (10/07/08 07:27 PM)
Edit Reason: add some info

Top
#181438 - 10/07/08 07:21 PM Re: Redundant Ground MC [Re: electure]
SolarPowered Offline
Member

Registered: 07/05/04
Posts: 615
Loc: Palo Alto, CA, USA
According to http://www.afcweb.com/faq_.html

Quote:
What's the difference between HCF and MC cable?

The difference between HCF and MC cables (as manufactured by AFC Cable Systems) is the grounding capabilities of the cable assemblies.

Type HCF cable has a green grounding conductor plus the armor/bond wire combination, thereby providing redundant or isolated grounding capability. HCF is a Type AC cable and is manufactured in accordance with U.L. 4.

Perhaps someone else manufactures an HCF cable that's type MC.

Top
#181440 - 10/07/08 07:34 PM Re: Redundant Ground MC [Re: SolarPowered]
SolarPowered Offline
Member

Registered: 07/05/04
Posts: 615
Loc: Palo Alto, CA, USA
Too late to edit my previous post: Now that I'm thinking about it, I do recall an announcement a couple years ago that somebody was making an MC version of HFC.

Top
#181824 - 11/02/08 08:11 AM Re: Redundant Ground MC [Re: SolarPowered]
watersparkfalls Offline
Member

Registered: 03/08/05
Posts: 210
Loc: Washington...Not DC
I know this has been answered already but,
the idea of grounding with the conductors wouldn't work for two reasons. 1-its aluminum and conductors are copper and 2-that bonding jumper is very thin(16awg ?) and breaks very easily...but diffrent metals cant be tied directly tgether.

H20

Top
#181827 - 11/02/08 08:51 AM Re: Redundant Ground MC [Re: watersparkfalls]
gfretwell Online   content


Member

Registered: 07/20/04
Posts: 9065
Loc: Estero,Fl,usa
The bonding conductor in the new MC cable is not that little strip you had in type AC. This is larger than the circuit conductors and in tight contact with the armor
_________________________
Greg Fretwell

Top