The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Forum Software Upgrade coming soon...
by gfretwell
01/17/17 01:16 PM
Why cables look like they do
by Texas_Ranger
01/17/17 12:33 PM
Re: Fabricating Guards out of Lexan?
by ghost307
01/17/17 11:21 AM
Would ELV branch circuits be a good idea?
by ghost307
01/17/17 11:18 AM
100% breakers?
by Texas_Ranger
01/16/17 06:13 AM
New in the Gallery:
Desk-mounted "power-board"
Shout Box

Top Posters (30 Days)
HotLine1 19
Webmaster 14
Trumpy 12
ghost307 12
gfretwell 10
Who's Online
2 registered (ghost307, gfretwell), 0 Guests and 78 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#181422 - 10/07/08 09:36 AM 75KVA Auto Transformer
mr_electrician Offline
Member

Registered: 06/22/07
Posts: 106
Loc: London, Ontario
I have been asked to temporarly hook up a piece of equipment. It is 480V 3 phase and has 90A fuses on its main disconnect. The majority of the load is the electric heaters. I have a 75 KVA auto transformer (600/480) that I am going to use. We have a 600V service. I was wondering if anyone has had any issues trying to power up a 75KVA transformer with 60A primary fuses on it. I want to disconnect the electric heaters on the piece of equipment for now since we are onlyy worried about testing the other connected loads such as motors and I/O. This would leave a very small connected load but I am worried that the inrush of the transformer would blow the 60 amp fuses. Should I be safe and fuse it at 80 amps as if it were fully loaded?
_________________________
Never trust an electrician with no eyebrows!!

Top
2017 / 2014 NEC & Related Books and Study Guides
#181448 - 10/08/08 09:49 AM Re: 75KVA Auto Transformer [Re: mr_electrician]
mikesh Offline
Member

Registered: 06/07/06
Posts: 614
Loc: Victoria, BC, Canada
I have an installation here that powers a 75 KVA transformer with 60A Time delay fuses The run to the transformer is long, more than 100 meters. 60 Amp fuses were chosen because the secondary powers a 200 amp panel and there is no secondary OC protection so 60 A was the biggest fuse that could match without another OC device on the secondary or a 225 amp panel. They have been operating for about 2 1/2 years without an inrush failure on these fuses. I do think the impedance of the run helps too

Top
#181449 - 10/08/08 09:50 AM Re: 75KVA Auto Transformer [Re: mr_electrician]
mr_electrician Offline
Member

Registered: 06/22/07
Posts: 106
Loc: London, Ontario
So those who are interested know, I went ahead and strangled the 75KVA transformer primary to 60A and it held when I turned it on. So I guess now I can go ahead and start seeing what does and doesn't work on this boat anchor. Did I mention that it has sat for 2-3 years with no power to it. Allready I have to reload the plc program. Battery went dead!!
_________________________
Never trust an electrician with no eyebrows!!

Top


ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals