#181371 - 10/05/08 07:37 PM Shared neutral and 2 GFI circuits
Grover Offline
Member
Registered: 01/19/05
Posts: 109
Loc: Sebago, ME, USA
Can I run 12/3 across a garage, overhead to a basement, and then use this shared neutral to feed 2 GFI proctected dircuits? Pigtail the neutral to go to each separate circuit - each having 2-3 outlets - unknown and variable loads - depending on homeowner.

Breaker will be a 2 pole 20 - yoked - common trip.

Each GFI will compare incoming - red or black - with neutral, and will be independant of the load on the other red or black feed. Right?

So if the load on the black is 6A and the load on the red is 10A what happens? In this case, does the GFI device look only "downstream", or does it look "upstream" as well - that is, does it see the imbalance at the pigtail, or only on the load side of the device?

Or do I need a 2 pole GFI breaker?

Thanks!

Grov
Top
Work Gear for Electricians and the Trades
#181373 - 10/05/08 09:22 PM Re: Shared neutral and 2 GFI circuits [Re: Grover]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9036
Loc: Estero,Fl,usa
A gfci does not look at anything on the line side of the device. As long as you split out your multiwire before you feed the GFCIs you will be fine
_________________________
Greg Fretwell
Top
#181378 - 10/06/08 04:18 AM Re: Shared neutral and 2 GFI circuits [Re: gfretwell]
wire_twister Offline
Member
Registered: 07/25/07
Posts: 265
Loc: Georgia USA
2 pole GFCI breaker will not work in that application, stick with the receptacles they will work for you.
_________________________
Jimmy

Life is tough, Life is tougher when you are stupid
Top
#181379 - 10/06/08 04:56 AM Re: Shared neutral and 2 GFI circuits [Re: wire_twister]
Grover Offline
Member
Registered: 01/19/05
Posts: 109
Loc: Sebago, ME, USA
Thanks guys!

Grov
Top
#181380 - 10/06/08 06:24 AM Re: Shared neutral and 2 GFI circuits [Re: Grover]
JBD Offline
Member
Registered: 07/12/01
Posts: 599
Loc: WI, USA
Actually, a 2-pole GFCI would work in your case, but there is no need to use one. Your GFCI receptacles idea is just fine.

GFCI's simply look at the total amount of current that flows out of their load terminals and compare it to the total amount that flows back in.
Top
#181475 - 10/11/08 02:51 AM Re: Shared neutral and 2 GFI circuits [Re: JBD]
Texas_Ranger Offline
Member
Registered: 12/17/01
Posts: 2391
Loc: Vienna, Austria
After all your 120/240 3 wire feeder is just like what feeds your main panel, so what should be the problem?
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (cableguy619), 64 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals