The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Correct rotation, wrong sequence
by Potseal
Yesterday at 03:14 PM
Industrail Control Panel bonding per 409.108
by sparkyinak
12/09/16 06:29 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 11
HotLine1 9
Potseal 9
sparkyinak 8
Texas_Ranger 7
Who's Online
0 registered (), 8 Guests and 1 Spider online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#181140 - 09/23/08 05:26 PM GE radial wiring system from 1930s
Albert Offline
Member

Registered: 08/16/06
Posts: 76
Loc: Falls Church, VA
In the 1936 General Electric Supply Corp. wiring materials catalog, more than a dozen pages at the front of the book are devoted to promoting the "radial wiring system" for residences.

Essentially, the system was an extreme version of the concept of feeders and subpanels, with the important difference that the feeders are not fused and therefore had to follow the NEC tap rules. I'm not an electrician and am not familiar with the current code, but at the time the rules were that taps may be no longer than 25 feet, must terminate at a single set of fuses/breakers, and must have a capacity of at least one third of the main fuse/breaker.

The branch circuit breakers at the end of the feeders were installed like toggle switches in standard single or multi-gang outlet boxes with raised covers.

The service-entrance panel was dubbed the "totalizing unit". It consisted merely of a main pull-out fuse block, plus fuse blocks for the range and other special loads. All of the feeders were connected directly to busbars on the load side of the main fuses.

Albert LaFrance

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#181141 - 09/23/08 05:30 PM Re: GE radial wiring system from 1930s [Re: Albert]
EV607797 Offline
Member

Registered: 10/25/06
Posts: 756
Loc: Fredericksburg, VA, USA
I sure would love to see those pages, Albert. Any chance that you might be able to scan them or post a link?
_________________________
---Ed---

"But the guy at Home Depot said it would work."

Top
#181144 - 09/23/08 06:12 PM Re: GE radial wiring system from 1930s [Re: EV607797]
electure Offline

Member

Registered: 12/24/00
Posts: 4226
Loc: Fullerton, CA USA
It's not a whole heck of a lot different from 1935 until now.

From (2008) NEC 240.21(B)


(2) Taps Not over 7.5 m (25 ft) Long. Where the length of
the tap conductors does not exceed 7.5 m (25 ft) and the tap
conductors comply with all the following:
(1) The ampacity of the tap conductors is not less than
one-third of the rating of the overcurrent device protecting
the feeder conductors.
(2) The tap conductors terminate in a single circuit breaker
or a single set of fuses that limit the load to the ampacity
of the tap conductors. This device shall be permitted
to supply any number of additional overcurrent devices
on its load side.
(3) The tap conductors are protected from physical damage
by being enclosed in an approved raceway or by other
approved means.

Top
#181146 - 09/23/08 06:58 PM Re: GE radial wiring system from 1930s [Re: EV607797]
Albert Offline
Member

Registered: 08/16/06
Posts: 76
Loc: Falls Church, VA
 Originally Posted By: EV607797
I sure would love to see those pages, Albert. Any chance that you might be able to scan them or post a link?


Sure, I'd be glad to scan them - I'll be pretty busy for the next few days, but should be able to get to it by next week. Feel free to remind me if I forget!

Top
#181149 - 09/23/08 07:38 PM Re: GE radial wiring system from 1930s [Re: Albert]
EV607797 Offline
Member

Registered: 10/25/06
Posts: 756
Loc: Fredericksburg, VA, USA
I'm not interested in the code comparison to today's standards. I am simply interested in old "technology" advertising, that's all.

I did a Google search of "GE Radial Wiring" and enjoyed the old advertising. Unfortunately, being able to read the full text required purchasing a membership. I'm interested, but not that interested.