I bought an older house/cottage which has 2-wire service from the utility pole. My panel is a Cutler-Hammer model which has 2 60-amp breakers (connected with a bar) as the main disconnect. There is also a 240v electric range wired to the panel.
How is this possible? I have read that 2-wire service only allows for 120v service. The range is connected as follows: a red and a black wire connected to a twin breaker (looks just like the main disconnect), and a white neutral connected to the neutral bus.
What kind of service do I have? 60A or 120A? 120V or 240V?
Thanks
Top
Work Gear for Electricians and the Trades
#18105 - 12/05/02 08:27 PM Re: Need advice
Wirenuttt Offline
Member
Registered: 11/10/02
Posts: 267
Loc: Massachusetts
I beleive your right without looking at it. You have an old 120 volt system which originally was probably a 30 amp service. Whoever tied those 240 volt appliances in, cheated. I highly recommend that you replace this to at least a 100 amp service which includes a grounding system. I'm surprised the home inspector didn't notice this. If you don't have the majority of your major appliances on gas u may want to consider 200 amp service. Hope this helps
Top
#18106 - 12/05/02 08:33 PM Re: Need advice
caselec Offline
Member
Registered: 04/14/02
Posts: 558
Loc: San Jose, CA
Are there 2 insulated wires and 1 bare wire feeding your house? Or 1 insulated wire and 1 bare wire?
_________________________
Curt Swartz
Top
#18107 - 12/05/02 08:40 PM Re: Need advice
electrical dummy Offline
Junior Member
Registered: 12/05/02
Posts: 4
There are 2 insulated wires and 1 uninsulated wire. I assumed that the uninsulated wire is only there to provide physical support to the insulated ones. Is this actually a neutral, and I have 3-wire service?
Top
#18108 - 12/05/02 08:49 PM Re: Need advice
sparky66wv Offline
Member
Registered: 11/17/00
Posts: 2232
Loc: West Virginia
<jumping in>
Yes, the bare cable is indeed the grounded conductor or "neutral".

You have a 120/240V service.

</jumping in>



Didn't mean to barge in when it suddenly became an easy answer!
_________________________
-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
Top
#18109 - 12/05/02 08:54 PM Re: Need advice
electrical dummy Offline
Junior Member
Registered: 12/05/02
Posts: 4
Cool.
Is it 120 amp service then, based on the main disconnect as I described above?
Top
#18110 - 12/05/02 09:34 PM Re: Need advice
sparky66wv Offline
Member
Registered: 11/17/00
Posts: 2232
Loc: West Virginia
No, most definitely a 60A, the current remains consistant, unless there are 2 double pole breakers tied together, a la GE 200A, but it would be plainly marked at the correct current rating.

I agree with the above posts that an upgrade to 200A should be considered.

[This message has been edited by sparky66wv (edited 12-06-2002).]
_________________________
-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
Top

Member Spotlight
Member Since: 01/22/05
Posts: 5316
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 65 Guests and 12 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals