The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
10/24/16 08:46 PM
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 7
ghost307 7
renosteinke 6
Potseal 4
Who's Online
0 registered (), 302 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#180932 - 09/17/08 03:12 AM Is there enough capacity?
schenimann Offline

Registered: 02/18/08
Posts: 194
Loc: Western North Carolina
I had a post last month about 180 amp heat strips in a plant we work in. I went yesterday to talk more about the job with them. They potentially have five of these setups which would be 900 amps. They asked me if there was enough capacity with the existing service to handle this.

It is a 80 year old thread plant. I am trying figure out a way to determine their capacity.

Could I look at their power usage over the last year and compare that to their current service size and capacity to determine what they are using or is this the wrong approach. Do I need to physically monitor power for different panels and do a load calculation? If so, what is the best equipment for this?

I know some of of you guys do this sort of thing. Your help is appreciated.

Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#180933 - 09/17/08 03:37 AM Re: Is there enough capacity? [Re: schenimann]
SteveFehr Offline

Registered: 03/19/05
Posts: 1192
Loc: Chesapeake, VA
The kWh on the power bill may give you an idea, but you can only calculate the average demand, and not peak current. Has the meter recorded peak current demand? If not, that's your first step. The best way is to hook up a power quality analyzer (or similar) on their service and leave it there for a year. That will tell you peak demand, as well as a wealth of other information like power factor and transients.

Even this analysis doesn't give the true full picture; I will never design to more than 80% capacity to allow for unplanned surge.

A spot check with an ammeter may give you an idea of capacity, and in some cases may be good enough (if they have a 3000A service and 100A of load, I think you're OK.) It may also give you an easy "no" answer if they're drawing 1200A on a 1500A service. But if it's in between, you must consider that HVAC load can be more than the rest of the building put together, yet only shows up on the hottest/coldest days of the year.


ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals