The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Temporarily feeding a panel...
by ghost307
Today at 03:23 PM
Locked rotor, no burnout
by jraef
Today at 01:18 PM
Massive power outage South Australia
by Meadow
Today at 06:46 AM
short circuit??
by Meadow
Today at 06:43 AM
Norwegian power?
by Meadow
Today at 06:36 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 13
sparky 10
sparky66wv 8
gfretwell 8
Vlado 6
Who's Online
0 registered (), 81 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#180811 - 09/11/08 01:11 PM Service Entrance Grounding
thiggy Offline
Member

Registered: 05/12/04
Posts: 25
Loc: B'ham Al
While examining my mother's fuse panel, I started wondering about the grounding system. Her house was built about 1960, and has a 100 amp fuse box on the inside basement wall, with a 100 amp cartridge fuse disconnect outside beside the meter. I noticed that the outside box has a bare ground wire which runs in to the fuse box, then up to the cold water copper tubing which runs above the fuse box. There is no ground rod driven into the soil. Is this an appropriate method of grounding the service panel? I wonder about the continuity of the copper plumbing, particularly where there is a pressure regulator in the line. Should this go to a ground rod in the soil rather than being clamped to the water system?

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#180812 - 09/11/08 01:30 PM Re: Service Entrance Grounding [Re: thiggy]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9012
Loc: Estero,Fl,usa
Back when all water distribution was metal that was the best grounding electrode. The whole city was tied to the same equipotential grid. Now that everything is plastic that is no longer true so we have the requirement for the supplemental electrode. I would drive a rod and connect it to the panel. If there is any question about the conductivty of the pressure regulator (not all metal body) jumper around it.
_________________________
Greg Fretwell

Top