#180811 - 09/11/08 01:11 PM Service Entrance Grounding
thiggy Offline
Member
Registered: 05/12/04
Posts: 25
Loc: B'ham Al
While examining my mother's fuse panel, I started wondering about the grounding system. Her house was built about 1960, and has a 100 amp fuse box on the inside basement wall, with a 100 amp cartridge fuse disconnect outside beside the meter. I noticed that the outside box has a bare ground wire which runs in to the fuse box, then up to the cold water copper tubing which runs above the fuse box. There is no ground rod driven into the soil. Is this an appropriate method of grounding the service panel? I wonder about the continuity of the copper plumbing, particularly where there is a pressure regulator in the line. Should this go to a ground rod in the soil rather than being clamped to the water system?
Top
Work Gear for Electricians and the Trades
#180812 - 09/11/08 01:30 PM Re: Service Entrance Grounding [Re: thiggy]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9066
Loc: Estero,Fl,usa
Back when all water distribution was metal that was the best grounding electrode. The whole city was tied to the same equipotential grid. Now that everything is plastic that is no longer true so we have the requirement for the supplemental electrode. I would drive a rod and connect it to the panel. If there is any question about the conductivty of the pressure regulator (not all metal body) jumper around it.
_________________________
Greg Fretwell
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Looking for older post
by sparkyinak
Today at 12:27 AM
License exam
by TRUE POWER
Yesterday at 11:33 PM
Members: Non-Members: Did you know?
by Admin
Yesterday at 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM
International Wire Colour Codes
by Texas_Ranger
01/21/17 03:29 PM

Who's Online
1 registered (Admin), 89 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Member Since: 08/01/07
Posts: 62

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals