The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
International Wire Colour Codes
by Texas_Ranger
Today at 08:24 AM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
230 or 345 kV transmission lines?
by annemarie1
10/12/16 01:23 PM
New in the Gallery:
12.5A through 0.75mm flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 11
HotLine1 6
renosteinke 6
ghost307 5
Potseal 4
Who's Online
1 registered (hyetal), 201 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#180810 - 09/11/08 12:54 PM SER Cable
George Little Offline

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
As an inspector, have you ever had a person want to install SER cable in conduit - underground? I wrote this up and the contractor insisted that first of all, he has never been written up on that before and secondly that the conductors were Listed XHHW so what's the problem?

So he offered to remove the jacket. Now we have a bare aluminum EGC in conduit in the ground.

Comments are invited.
George Little

2014 / 2011 NEC & Related Books and Study Guides
#180813 - 09/11/08 01:45 PM Re: SER Cable [Re: George Little]
KJay Offline

Registered: 11/27/07
Posts: 763
Loc: MA, USA
I’m not an inspector, but I can understand your frustration. I swear to god we must have covered this in every code cycle seminar I’ve been to for at least the last ten years. I have seen guys do this before, but not for many years. I guess the word still hasn’t gotten out to everyone.

Here is what the 2007 UL White book has to say:

Type SE— Indicates cable for aboveground installation. Both the individual insulated conductors and the outer
jacket or finish of Type SE are suitable for use where exposed to sun. Type SE cable contains Type RHW,
RHW-2, XHHW, XHHW-2, THWN or THWN-2 conductors.

#180814 - 09/11/08 01:51 PM Re: SER Cable [Re: KJay]
Ralpha494 Offline

Registered: 05/19/04
Posts: 71
Loc: Pewaukee,WI,USA
338.12 Uses not permitted
(A)SE Cable
(2) Underground with or without a raceway

#180817 - 09/11/08 03:11 PM Re: SER Cable [Re: Ralpha494]
renosteinke Offline
Cat Servant

Registered: 01/22/05
Posts: 5305
Loc: Blue Collar Country
Which brings us back to stripping the cable off ....

Assuming the conductors are individually marked as to the insulation type, there's no violation. Nor is there any requirement that the ground wire be insulated.

However, it's likely that the individual wires are not marked - just the outer jacket. Remove the jacket, remove the listing.

Then there is the matter of aluminum in contact with the earth. Not allowed by code ... but is 'in the pipe' the same as 'in contact with earth?'

#180819 - 09/11/08 04:57 PM Re: SER Cable [Re: renosteinke]
EV607797 Offline

Registered: 10/25/06
Posts: 756
Loc: Fredericksburg, VA, USA
Excellent subject resurrection. I've butted heads with inspectors in my younger days about this, but now that I've matured a bit, I see where I was wrong. My last argument with an inspector yielded the most logical answer. I couldn't seem to understand the harm in running 6/3 Romex in a conduit for a short distance to a detached garage.

His answer was fairly simple and it certainly shut me up on this subject forever. A conduit in the ground is never dry and Romex is not approved for wet locations. People really do go around with the misconception that glued PVC is water-tight. Nothing could be farther from the truth.

"But the guy at Home Depot said it would work."

#180820 - 09/11/08 05:03 PM Re: SER Cable [Re: EV607797]
sparkyinak Offline

Registered: 07/08/07
Posts: 1288
Loc: Alaska
I can see the both sides of the argument. SE is not for sub subsurface use, xhhw is. What a paradox. \:\)
"Live Awesome!" - Kevin Carosa

#180822 - 09/11/08 06:24 PM Re: SER Cable [Re: sparkyinak]
KJay Offline

Registered: 11/27/07
Posts: 763
Loc: MA, USA
Just to be sure, I went and stripped off about 3-feet of jacket on some aluminum SE and SER cables I have in stock and I couldn’t find any markings on the individual conductors, not even a voltage rating.

It seems that stripping the jacket off SE cable and using the unmarked conductors in that manner would be on par with stripping the sheath off NM-B cable and using the unmarked conductors for wiring up a #2 fuel oil pump, because we are sure they are gas and oil resistant THHN insulation. \:D

#180824 - 09/11/08 07:54 PM Re: SER Cable [Re: KJay]
gfretwell Offline


Registered: 07/20/04
Posts: 9023
Loc: Estero,Fl,usa
If you set the way back machine to about a year ago you will see a thread I started about this. The #2 copper SER we had was marked THWN conductors on the jacket, nothing on the conductor. (I still have about 20-30' left over)

I am not sure what we decided here but the inspector didn't even blink. We were OK and off we went.
Greg Fretwell

#180826 - 09/11/08 08:46 PM Re: SER Cable [Re: gfretwell]
KJay Offline

Registered: 11/27/07
Posts: 763
Loc: MA, USA
Greg, I read the old posts. It sounds like something right out of a Three Stooges skit, with the golf cart and all the pushing and pulling.
I think maybe that inspector should hang up his spurs and go back to sawing roast beef at Arby’s. Around here, he would have gotten the “Paper Hat” award for letting that one slip by. \:D \:D

#180831 - 09/12/08 03:42 AM Re: SER Cable [Re: KJay]
SteveFehr Offline

Registered: 03/19/05
Posts: 1192
Loc: Chesapeake, VA
Sounds rather like the health dept people who will let you add bedrooms to a house on septic, but you can't have any closets in the bedrooms.