The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
10/24/16 08:46 PM
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 7
ghost307 7
renosteinke 6
Potseal 4
Who's Online
0 registered (), 133 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#18056 - 12/05/02 02:12 PM wiring panel surge devices
donles Offline

Registered: 04/28/01
Posts: 82
Loc: Bridgeville, PA USA
When you wire a panel surge device, do you connect to the terminals of an existing two-pole breaker? Does the Code address this?
I got a call to check-out some electrical issues brought up by a home inspector. One issue was two wires to a breaker's terminals and I found the additional wires to be the two "hot" wires from the supressor. There is not room in the panel for a two-pole breaker dedicated to the supressor. Since the supressor is not a "load", I wouldn't think that it would matter if it's terminated on a breaker's load terminals along with the actual load, as long as it's a 15 amp breaker because the supressors wires look to be 14 AWG. . Hopefully, someone will say if it's a code issue.
A separate matter is that the breaker the supressor is connected to is the main breaker in a GE split bus-panel, so it's really the unprotected line terminals on the breaker. If someone chimes in and says it's OK to connect to a branch circuit breaker, I will move the wires to 2 15 amp breakers. If not, I will remove the supressor. In any event it's coming off of the main.

Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#18057 - 12/05/02 02:30 PM Re: wiring panel surge devices
Electric Eagle Offline

Registered: 04/20/02
Posts: 928
Loc: Alpharetta, GA
Some breakers, such as Square D QO, are designed to accept 2 conductors of equal size. Most are not. I always give the TVSS its own breaker, most say to use a breaker 30 amp or less. Device wiring is allowed to be smaller than branch circuit wiring due to the short length. One option is to pigtail the TVSS with a 15,20,or 30 Double Pole, but make sure the device is rated for that breaker.