The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Locked rotor, no burnout
by andey
Today at 04:48 AM
Temporarily feeding a panel...
by Potseal
Yesterday at 11:05 PM
Massive power outage South Australia
by Meadow
Yesterday at 06:46 AM
short circuit??
by Meadow
Yesterday at 06:43 AM
Norwegian power?
by Meadow
Yesterday at 06:36 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 14
sparky 10
gfretwell 8
sparky66wv 8
Potseal 7
Who's Online
1 registered (jraef), 292 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#180482 - 08/27/08 12:25 PM NEMA 3R enclosure
sudsy4 Offline
Member

Registered: 04/24/02
Posts: 32
Loc: Elizabeth,PA USA
Can I come thru a wall into the back of a NEMA 3R enclosure mounted on the wall and maintain the 3R rating?

Thanks
_________________________
Bill

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#180484 - 08/27/08 01:11 PM Re: NEMA 3R enclosure [Re: sudsy4]
wire_twister Offline
Member

Registered: 07/25/07
Posts: 265
Loc: Georgia USA
If you use a myers hub.
_________________________
Jimmy

Life is tough, Life is tougher when you are stupid

Top
#180485 - 08/27/08 02:56 PM Re: NEMA 3R enclosure [Re: wire_twister]
renosteinke Offline
Cat Servant
Member

Registered: 01/22/05
Posts: 5300
Loc: Blue Collar Country
To answer that, you need to understand how the enclosures are tested.

For the NEMA-3R test, a driving rain is sent onto the enclosure at about a 15 degree angle. At the end of the test, there cannot be a 'significant' amount of water in the enclosure.

In addition, there is a rule that factory KO 'pre-punches' cannot be located higher than the lowest energized part.

Some understand the latter rule to mean that ANY opening made above the lowest energized part has use a Myers' hub. I'm not convinced of that logic for vertical faces, though I agree when the opening is on the top face. (After all, snow and water can accumulate on the top).

For openings on protected faces - like the back - I have a bit of trouble imagining how any significant amount of water can ever reach the opening - let alone enter it.

Remember ... NEMA-3R is essentially a glorified umbrella; it's not intended to protect a directed water source, such as a hose stream.

Top
#180487 - 08/27/08 03:18 PM Re: NEMA 3R enclosure [Re: renosteinke]
sparkyinak Offline
Member

Registered: 07/08/07
Posts: 1286
Loc: Alaska
I agree with Reno. The hole on top of some 3R's enclosures has that up rolled lip to prevent wat to get into the enclosure.
_________________________
"Live Awesome!" - Kevin Carosa

Top
#180495 - 08/27/08 06:30 PM Re: NEMA 3R enclosure [Re: sparkyinak]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9012
Loc: Estero,Fl,usa
Don't we go in the back of meter cans all the time? I don't remember any special fitting.
_________________________
Greg Fretwell

Top
#180498 - 08/27/08 08:00 PM Re: NEMA 3R enclosure [Re: gfretwell]
sparkyinak Offline
Member

Registered: 07/08/07
Posts: 1286
Loc: Alaska
The special fittings were for "field expediant" holes not factory KO's
_________________________
"Live Awesome!" - Kevin Carosa

Top
#180542 - 08/29/08 08:57 AM Re: NEMA 3R enclosure [Re: sparkyinak]
JValdes Offline
Member

Registered: 06/03/07
Posts: 308
Loc: South Carolina
You can use a nipple or conduit in the back bottom factory KO and maintain the rating. If its a concentric KO, and you have any rings left you must bond with a bonding bushing. Not required with PVC of course.

Top
#180545 - 08/29/08 10:39 AM Re: NEMA 3R enclosure [Re: JValdes]
electure Offline

Member

Registered: 12/24/00
Posts: 4225
Loc: Fullerton, CA USA
 Quote:
If its a concentric KO, and you have any rings left you must bond with a bonding bushing


JV, Unless it's service equipment (or you really blow out the concentric KO's), they're not required on systems for under 250 volts to ground.

Top