#180414 - 08/25/08 11:15 AM Securing lay in light fixtures
sparkync Offline
Member
Registered: 10/17/02
Posts: 812
Loc: NC
Somehow I was under the impression that lay in light fixtures had to be secured by individual wires from a main support above the ceiling. I'm aware that they are to be secured to the "framing members" by screws, rivets, etc....
I'm looking in the 2005 code and that's all I see. Am I missing something? Thanks, Steve....
Top
2017 / 2014 NEC & Related Books and Study Guides
#180418 - 08/25/08 11:59 AM Re: Securing lay in light fixtures [Re: sparkync]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6776
Loc: Brick, NJ USA
Steve:
NEC says what you listed above. Seismic code/building or fire may require independent support. Lastly, plans may require it in the spec; or the ceiling grid mfg may have it in the mfg installation instructions.
_________________________
John
Top
#180429 - 08/26/08 06:49 AM Re: Securing lay in light fixtures [Re: HotLine1]
Zapped Offline
Member
Registered: 10/01/02
Posts: 482
Loc: Huntington Beach, CA, USA
HotLine's got it right, especially out here on the West coast. Your building and seismic codes dictate much more of the overhead support requirements than your NEC and electrical inspector.

If there is any question about the requirements in your area, contact your AHJ as early in the job as possible to avoid going back for a red tag from someone you don't expect.

Good Luck!
Top
#180600 - 08/31/08 06:50 PM Re: Securing lay in light fixtures [Re: Zapped]
Yoopersup Offline
Member
Registered: 03/04/03
Posts: 822
Loc: Michigan
300.11 (A) 1(Fire -Rated assemblys ) 300.11 (A) 2 Non-Fire -rated. Handbook covers it quite well,
also 410.16.
More or Less says UNLESS ceiling assembly has been Tested and Listed for that use. Support wires are required & must be marked by color or tagging.
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 52 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals