I've heard about buildings in heavily loaded downtown areas served with what's called a "network service." To me, I look at this setup as as a system of large vault type transformers installed in the street that are paralleled onto the secondary mains and connected with a special switch called a "network protector." I've seen a special kind of electric meter called a "self contained network meter" and needs a fifth terminal? What is the difference between a 120/208 Y network service and a standard 120/208 Y service? I don't understand why a service like this needs a special meter. Perhaps I've got it confused.

If anyone can explain this to me I'd be most greatful. Thanks.
Top
Work Gear for Electricians and the Trades
#180215 - 08/18/08 08:05 AM Re: Network meters; network service [Re: junkcollector]
winnie Offline
Member
Registered: 09/15/03
Posts: 649
Loc: boston, ma
You may be encountering different uses of the term 'network service', with entirely different meanings.

I have seen the term used to describe 120/208 'single phase' service, such as might be used for individual residences in an apartment building. Such a service is really two legs of a 208/120 wye, and so at the basic physics level is not really 'single phase'; but is used in the same fashion as a residential single phase service.

As to why two legs of a 120/208 service requires a different meter from a 120/240 service: A standard meter for 120/240 single phase service 'cheats' and is not 'blondel compliant'. The 'blondel theorem' basically says that to correctly meter a three wire service you need to make _two_ voltage measurements (say the two leg-neutral voltages), and _two_ current measurements (say the two 'hot' leg currents). A standard 120/240 meter simply makes one voltage measurement (the leg-leg voltage) and then assumes that the leg-neutral voltage is exactly 1/2 of this value. In other words the meter ignores any phase difference or imbalance.

Because of the phase difference present in a two leg 120/208 service, such a meter would read anywhere up to 14% low, not accurate enough for utility metering.

-Jon
Top
#180218 - 08/18/08 04:26 PM Re: Network meters; network service [Re: winnie]
junkcollector Offline
Member
Registered: 04/15/07
Posts: 36
Loc: Central MN
Thanks for the explanation.cool

Basically what you are saying is that you need a meter with two voltage coils, and have each coil connected between the neutral and each hot leg. I would imagine that the neutral would get connected to the sideways fifth terminal, instead of with a standard 120/240 v where the meter is not connected to the nuetral at all (one voltage coil that gets 240, connected to L1 & L2)

That makes sense. Thanks again.
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 43 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
KrmtFrg, Stack, Scotto, Freecrowder, clee512

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals