#180169 - 08/15/08 01:52 PM Insta-Hot breakers
wiking Offline
Junior Member
Registered: 12/13/02
Posts: 32
Loc: Florida, USA
For years I have always up sized the breaker by at least 125% of the load on an Insta-Hot (sometimes known as a Tankless Water Heater). Now I find out that since it is considered a non-continuous load, I can size the breaker according to the load, at least according to one supplier and a company tech rep I talked to.
This would have made things much easier if I had known this, but am glad I know now.
Doesn't it seem to be pushing it too close to have the breaker right at the amp load? What about nuisance tripping in case of a weaker or eventually worn breaker?
Factor in things like voltage drop or perhaps the device slightly raising it's ampacity over time due to wear or tear, it seems like a potential for at least some minor problems.
Another question I have is whether a disconnect is required under the sink with the Insta-Hot. A well respected (and feared by some) inspector told me that if there was not a requirement on the blueprint for a disconnect, it doesn't need one according to code. I definitely always label the breaker in the panel and write on the insta hot what circuit and panel it is.
Top
2017 / 2014 NEC & Related Books and Study Guides
#180184 - 08/16/08 05:13 AM Re: Insta-Hot breakers [Re: wiking]
Tom Offline
Member
Registered: 01/01/01
Posts: 1044
Loc: Shinnston, WV USA
Your supplier & tech rep are correct about circuit sizing. See 422.10

The circuit breaker can sevre as the disconnecting means but will probably need a provision for attaching a padlock and the provision must remain in place with or without the padlock. 422.31(B)
_________________________
Few things are harder to put up with than the annoyance of a good example.
Top
#180196 - 08/16/08 09:35 AM Re: Insta-Hot breakers [Re: Tom]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9036
Loc: Estero,Fl,usa
Around here they will usually want the local disconnect. Our AHJs do not think much of residential LOTO capabilities. Up to 20a this is usually cord and plug, 25a and up is going to be a pullout or switching device.
_________________________
Greg Fretwell
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6775
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 14 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals