The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Locked rotor, no burnout
by andey
09/30/16 04:48 AM
Temporarily feeding a panel...
by Potseal
09/29/16 11:05 PM
Massive power outage South Australia
by Meadow
09/29/16 06:46 AM
short circuit??
by Meadow
09/29/16 06:43 AM
Norwegian power?
by Meadow
09/29/16 06:36 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 14
sparky 10
sparky66wv 8
gfretwell 8
Potseal 7
Who's Online
2 registered (ghost307, cableguy619), 287 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#180123 - 08/13/08 07:45 PM Sizing for heatstrips
schenimann Offline
Member

Registered: 02/18/08
Posts: 194
Loc: Western North Carolina
I'm pricing out a job for a local plant. They had a gas heater go out and they are wanting to replace it with an electric heater to seee if there are any savings.

They are installing three sets of two 25kw heaters(480v). This is 60.1 amps per set. This is for 1 machine with the pontential of adding 5 more.

I'm feeding them from a busbar to a breaker panel to the heaters. I'm going to size my wire according to this number #6THHN.

Do I need to size my wire feeding the breakers at 180 amps or can I derate?

If I add another machine am I then up to 360 amps? Or five machines and 1080amps?

Thanks for your expertise.

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#180124 - 08/13/08 09:23 PM Re: Sizing for heatstrips [Re: schenimann]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9012
Loc: Estero,Fl,usa
I don't see any reason why you could use anything less than 100% of connected load and if this is continuous load it would be 125%.
_________________________
Greg Fretwell

Top
#180129 - 08/14/08 03:21 AM Re: Sizing for heatstrips [Re: gfretwell]
schenimann Offline
Member

Registered: 02/18/08
Posts: 194
Loc: Western North Carolina
Thanks Greg, I was going the wrong way with my size.

Top



ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals