The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
1 registered (geoff in UK), 133 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#179963 - 08/07/08 11:47 AM Low voltage lights under 30 volts
sparkync Offline
Member

Registered: 10/17/02
Posts: 811
Loc: NC
Sorry to be putting so many post. I guess it's my day in the shop and going over the code. One thing I wished they would have changed is 411.4(B). As far as I'm concerned and obviously a few of the inspectors I've had dealings with, the ruling for lights under 30 volts, to have to be
10 ft. away from a pool, is ridiculas. You can put a 120 volt light under the water. and within 5 ft., but you can't put a low voltage light within 10 ft. of the pool. I realize that the low voltage light is not grounded, but neither is it grounded when it is in the front or back yard after a hard rain and is accessible to children, elderly, etc. etc. It refers to article 680, but there is nothing I can find about low voltage lights in 680. I've had more than one pool where it was pratically impossible to keep that distance. I've had at least 2 inspectors that agreed with me. Anybody else had this problem. Seems like it just creats confusion, at least on my part it does...
Sorry for the ranting... guess it's just my day... Steve..

Top
2014 / 2011 NEC & Related Books and Study Guides
#179977 - 08/07/08 04:35 PM Re: Low voltage lights under 30 volts [Re: sparkync]
EV607797 Offline
Member

Registered: 10/25/06
Posts: 756
Loc: Fredericksburg, VA, USA
You aren't being ridiculous, Steve. I agree that this is downright silly. Then again, I think that lots of '08 changes are crazy. It screams of how much influence that the manufacturers have over the code. I'll bet that if any manufacturers of LV lighting had a seat on the NEC's board, this wouldn't be an issue at all.
_________________________
---Ed---

"But the guy at Home Depot said it would work."

Top
#179987 - 08/07/08 10:49 PM Re: Low voltage lights under 30 volts [Re: EV607797]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
If you had the same grounding and bonding requirement on a Malibu light as you have for an underwater light I am sure it would be safe.
_________________________
Greg Fretwell

Top
#181925 - 11/09/08 09:24 AM Re: Low voltage lights under 30 volts [Re: gfretwell]
harold endean Offline
Member

Registered: 02/16/02
Posts: 2248
Loc: Boonton, NJ
What does the manufacture instructions state? I have seen where the Manufactures instruction prohibits their lights within 10 feet of the pool. If that is the case, then they can't be there as per 110 of the NEC. Right? I am not saying that all manufactures do not allow their lights near the pool, just some of them.

Top
#181933 - 11/09/08 03:23 PM Re: Low voltage lights under 30 volts [Re: harold endean]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
680 trumps 110.3(B). If it is not actually listed 680 safe I don't care what a manufacturer says on the label.
_________________________
Greg Fretwell

Top
#182020 - 11/16/08 06:09 AM Re: Low voltage lights under 30 volts [Re: gfretwell]
sparky Offline
Member

Registered: 10/18/00
Posts: 5545
perhaps a gfi's efficy on the line side of the low v x-former is a consideration here?


Edited by sparky (11/16/08 06:09 AM)

Top
#182036 - 11/16/08 11:17 AM Re: Low voltage lights under 30 volts [Re: sparky]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
A ground fault on the secondary of a LV lighting transformer will not trip a GFCI. In fact the "first fault" will not be seen at all. You will have just grounded what was an ungrounded source.
_________________________
Greg Fretwell

Top
#182048 - 11/16/08 03:22 PM Re: Low voltage lights under 30 volts [Re: gfretwell]
sparky Offline
Member

Registered: 10/18/00
Posts: 5545
ok gfretwell, so would this justify the spacing difference?

~S~

Top
#182060 - 11/16/08 10:54 PM Re: Low voltage lights under 30 volts [Re: sparky]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
Perhaps I didn't explain this clearly enough.
Low voltage lights are generally not GFCI protected, the primary protection will not protect for a fault on the secondary. If they did you could never keep those cheap Malibu lights burning. wink

I suppose if someone came out with a LV light that did have GFCI on the secondary side there would be a reason to reexamine this.
_________________________
Greg Fretwell

Top
#182061 - 11/16/08 11:45 PM Re: Low voltage lights under 30 volts [Re: gfretwell]
frenchelectrican Offline

Member

Registered: 02/06/03
Posts: 938
Loc: Wi/ Paris France { France for ...
That will be nice idea if someone get the GFCI work on secondary side of LV luminaires but IMO you will get more GFCI trips than it should be.

But what I heard but not confirmed and myself I did see that some of the LV transfomer some of them have secondary side is on isolated format.

Merci,Marc
_________________________
Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)


Top