#179726 - 07/29/08 09:38 AM Permanent wall penetration for temporary cables.
LarryC Offline
Member
Registered: 07/05/04
Posts: 780
Loc: Winchester, NH, US
What is the correct method to install a feed-thru thru a wall?

I am envisioning a 6" square box with a cover, on each side of the wall and 2 short pieces of 2" EMT connecting the two boxes.

The feed-thru would be used to run temporary power, communication cables, liquid lines, etc. Obviously the covers would be installed when the pass-thru is not in use.
One side of this feed-thru is in a conditioned space and the other side is the building's loading dock.

Thanks,

Larry C
Top
Work Gear for Electricians and the Trades
#179743 - 07/29/08 05:32 PM Re: Permanent wall penetration for temporary cables. [Re: LarryC]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6775
Loc: Brick, NJ USA
Larry:
Is it a fire-rated wall??
Condensation may also be an issue.
_________________________
John
Top
#179746 - 07/29/08 06:29 PM Re: Permanent wall penetration for temporary cables. [Re: LarryC]
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5316
Loc: Blue Collar Country
This is primarily a design issue, but a good one for discussion.

For a fire rated wall, the key is to restore / maintain the fire resistance of the wall. Even for a 'normal' wall, the idea is to keep noise, drafts, etc., from passing through.

The method you propose isn't bad ... though I would use 'running thread,' rather than trying to get nipples to to be the right size. I'm a bit puzzled as to why you would want two nipples though ... keep in mind that all conductors of a circuit need to be run in the same nipple, and that you need a partition between low voltage and power cables.

Easier to do, perhaps, is to install one of the commercially available fire-stop products. These are nicely made tubes, flanges on either side .... and large enough to pass your pipes through. You seal the remaining gaps with the appropriate products, and all is well.

How to make the necessary holes in the wall? A roto-hammer, with the appropriate core drill, makes easy work of the chore.
Top

Member Spotlight
Member Since: 07/05/02
Posts: 8211
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 42 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals