#17968 - 12/04/02 03:44 PM Load for feeder
sparkync Offline
Member
Registered: 10/17/02
Posts: 812
Loc: NC
On the Refrigerated building I spoke of recently, I wonder if someone can check my math on the load. I have:

2- 3 phase scroll type compressors with
a RLA of 12.2 amps ( 12.2 X 2)= 24.4
25% of largest motor = 3.5

2 unit coolers inside:
The fans in each unit pulls:3 amps
( 3 X 2 )= 6.0

The defrost cycle for each pulls:
11.7 amps( 2 X 11.7 ) = 23.4

VPL ( I'm not sure what this is) = .8
Anti-sweat heater = 1.47
5 - 100 watt. lights = 4.17

Total load = 63.74

Anybody see that I'm missing something??
I'm presuming the fans run all the time
inside, according to what the rep. said,
even when they are in defrost cycle??
I thought they stopped during defrost,
myself, maybe I misunderstood him. Hope this comes out like I got it typed and not jumbled up...Thanks for the input.. Steve
Top
Work Gear for Electricians and the Trades
#17969 - 12/05/02 10:33 AM Re: Load for feeder
mj Offline
Member
Registered: 06/10/02
Posts: 186
Loc: meriidian, ms
check your 3. phase math calculations, i thank you total load will be about 15 amps less
Top

Member Spotlight
Member Since: 12/24/00
Posts: 4259
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (Admin), 60 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Stack, Scotto, Freecrowder, clee512, Jdscott2005

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals