The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
230 or 345 kV transmission lines?
by Vlado
Yesterday at 09:33 AM
breaker meltdown
by crselectric
Yesterday at 12:42 AM
Electrical mast flashing product
by ThomasWinfrey
09/22/16 12:14 AM
What estimating software do you recommend?
by sparky
09/21/16 07:20 PM
"Dry Run" Inspection goes awry
by HotLine1
09/20/16 07:39 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 17
gfretwell 9
sparky 9
sparky66wv 8
Vlado 6
Who's Online
1 registered (Webmaster), 63 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#179650 - 07/25/08 02:13 PM Double up on a phase
wiking Offline
Junior Member

Registered: 12/13/02
Posts: 32
Loc: Florida, USA
I found a run that feeds three circuits of recepticles while sharing a neutral. The problem is that when I looked, the blue circuit is actually landed on the black phase, unbalancing the neutral I would imagine. Evidently it's been operating that way for awhile without any problems that are known about. It might help that the neutral is #10 on 20amp circuits, but are there any bad effects that might be coming about because of this?

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#179654 - 07/25/08 03:36 PM Re: Double up on a phase [Re: wiking]
SolarPowered Offline
Member

Registered: 07/05/04
Posts: 615
Loc: Palo Alto, CA, USA
The configuration you describe can result in as much as 40 amps on the #10 neutral, which is only allowed to carry 30 amps. So, yes, the installation is unsafe, and in violation of code.

Top
#179655 - 07/25/08 04:42 PM Re: Double up on a phase [Re: wiking]
junkcollector Offline
Member

Registered: 04/15/07
Posts: 35
Loc: Central MN
 Originally Posted By: wiking
The problem is that when I looked, the blue circuit is actually landed on the black phase...


So is it just doubled up on the same breaker (black and blue on the same breaker), or is the breakers on the same phase in the panel? If it is on the same breaker, then it is considered the same circuit and there isn't really a problem. I assume otherwise...
 Originally Posted By: wiking

Evidently it's been operating that way for awhile without any problems that are known about.


There probably wasn't enough load on the circuit to load the nuetral wire to the point of overheating.

let us know...


Edited by junkcollector (07/25/08 04:42 PM)

Top
#179656 - 07/25/08 04:47 PM Re: Double up on a phase [Re: junkcollector]
SolarPowered Offline
Member

Registered: 07/05/04
Posts: 615
Loc: Palo Alto, CA, USA
A clarifying question: It appears that you're saying that two of the three circuits (black and blue) actually land on the black phase. Is that correct? (That is what my above answer is based on.)

Top
#179671 - 07/26/08 06:12 AM Re: Double up on a phase [Re: SolarPowered]
wiking Offline
Junior Member

Registered: 12/13/02
Posts: 32
Loc: Florida, USA
To clarify, there are three circuits on three different breakers sharing one neutral. The black wire is on the black phase, red on red, but the blue wire is landed on a black phase breaker on the other side of the panel.
This also brings up another point that I see all the time. I was told when I first came up that on a three phase panel if you shared a neutral that it better go with it's specific group. For instance there is one neutral for circuits 1,3,5 if they went to the same place. I wasn't allowed to use the same neutral to share with, say, 1,3, and 11, which would give you a neutral that has a black, red and blue phase on it, even though the 11 is out of sequence.
Is this common or do you find it acceptable to share any circuit numbers as long as they don't double up the phase?

Top
#179672 - 07/26/08 06:54 AM Re: Double up on a phase [Re: wiking]
renosteinke Offline
Cat Servant
Member

Registered: 01/22/05
Posts: 5299
Loc: Blue Collar Country
Funny you should ask ....

Prior to the 2008 NEC, you could use any breaker combination- at least, strictly according to the rules. The 2008, however, wants them grouped together, on a three-pole breaker, and the four wires (including neutral) zip tied together in the panel.

Top
#179690 - 07/27/08 06:04 AM Re: Double up on a phase [Re: renosteinke]
electure Offline

Member

Registered: 12/24/00
Posts: 4225
Loc: Fullerton, CA USA
 Quote:
on a three-pole breaker,


See 210.4 Multiwire Branch Circuits

The requirement is for:
"(B) Disconnecting Means. Each multiwire branch circuit
shall be provided with a means that will simultaneously
disconnect all ungrounded conductors at the point where
the branch circuit originates."

That seems to allow the use of listed handle ties as well.

And (D) "Exception: The requirement for grouping shall not apply if the circuit enters from a cable or raceway unique to the circuit that makes the grouping obvious"

Top
#179691 - 07/27/08 07:04 AM Re: Double up on a phase [Re: electure]
leland Offline
Member

Registered: 08/20/07
Posts: 856
Loc: Lowell area, Ma. USA
210.4 (B)--
This is a common misconception. I've had many discussions on it.
The KEY: Common "DISCONNECT"- not trip.
Once this is pointed out I get the ole'..."Ohhh-Ya".

As far as "D", I still group a single conduit, For "Justin".. Just in case some one adds ckts to it.
How many times have you seen a pipe added to a disco,because it's closer,then conductors added to the original pipe?


Edited by leland (07/27/08 07:06 AM)

Top
#179692 - 07/27/08 11:02 AM Re: Double up on a phase [Re: electure]
renosteinke Offline
Cat Servant
Member

Registered: 01/22/05
Posts: 5299
Loc: Blue Collar Country
I can't argue with that, Scott. Perhaps it's my own bad grammar, but I have never made a distinction between a three pole breaker that had an internal trip mechanism, and one that had three handles tied together.

I agree that either would meet this particular code requirement.

I'm sure that everyone had already been grouping such conductors together, wherever possible. The 'common disconnect' is a new requirement, but not that big of a deal. Where practice gets changed is the requirement to literally tie the hots, as well as the neutral, together in their own bundle.
That's bound to be fun, especially in panels with only one neutral buss.

Top
#179700 - 07/27/08 06:12 PM Re: Double up on a phase [Re: renosteinke]
electure Offline

Member

Registered: 12/24/00
Posts: 4225
Loc: Fullerton, CA USA
John,
The price of a 3 Pole breaker with a common trip is substantially higher than 3 single pole units and a handle tie.