#179618 - 07/24/08 05:07 AM Emergency Circuit Questions NEC 700
cgw Offline
Member
Registered: 07/29/04
Posts: 133
Loc: Rochester NY
building with a generator which has separate emergency transfer switch/panelbd and standby transfer switch/panelboard.
Can the fire alarm system be connected to the emergency system or would it be considered legally required standby power?

A branch circuits for emergency lighting need to run a good distance down a hall which does not have a fire sprinkler system. 700.9(D)(1), assuming it applies to my building, does it apply to branch circuits? If so does anyone manufacture a 1 hour cable or protective system?
Top
2017 / 2014 NEC & Related Books and Study Guides
#179619 - 07/24/08 06:26 AM Re: Emergency Circuit Questions NEC 700 [Re: cgw]
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5316
Loc: Blue Collar Country
Connect the fire alarm wherever you like ... if it's a UL listed control panel / alarm system, it is already required to have, as part of the system, a 24 hr. back-up power supply (ie: big battery).
Top
#179620 - 07/24/08 06:58 AM Re: Emergency Circuit Questions NEC 700 [Re: cgw]
earlydean Offline
Member
Registered: 12/22/03
Posts: 751
Loc: Griswold, CT, USA
Fire Alarm Systems as covered in NFPA 72 require a secondary power supply, not an "emergency source", nor is it classed as a "legally required standby source". Fire alarm secondary power is usually accomplished via batteries. Check out Chapter 4 of NFPA 72.

Only those loads required to be emergency loads are allowed to be connected to emergency sources. (NEC 700.9(B))

So, no, you cannot use an existing emergency source for the fire alarm system.

However, there is not a prohibition for loads cannected to the "legally required standby source".

But, NFPA 72, in section 4.4.1.9.3.1 requires engine-driven generators to comply with NFPA 110, for a Type 10, Class 24, Level 1 System. Type 10 means the generator starts and transfers within 10 seconds. Class 24 means there is enough fuel to operate at full load for 24 hours. Level 1 systems shall be installed when failure of the equipment to perform could result in loss of human life or serious injuries.

And, NFPA 72 section 4.4.1.5.1 requires a four hour battery system if a prime mover provides the power for continuity of service.

So, the bottom line: Use batteries, forget the generator.
_________________________
Earl
Top
#179624 - 07/24/08 11:01 AM Re: Emergency Circuit Questions NEC 700 [Re: earlydean]
cgw Offline
Member
Registered: 07/29/04
Posts: 133
Loc: Rochester NY
Thanks for the heads up.
We will have battery backup and it looks like the power will be on the standby system vs. the emergency system.
Top
#179632 - 07/24/08 07:32 PM Re: Emergency Circuit Questions NEC 700 [Re: cgw]
cgw Offline
Member
Registered: 07/29/04
Posts: 133
Loc: Rochester NY
I still have the lighting circuits to run down the un-sprinklered hallway. Does anyone manufacture a 1 hour cable or protective system?
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6776
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 37 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals