#179402 - 07/10/08 05:52 PM DANGER Milbank meter sockets with lever bypass.
gfretwell Online   content


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
From Bryan Holland BHgravity here via email today


I hope to have more details about this by tomorrow.

First report indicates:

the meter socket in question was a 200 amp bypass type. labled with "3 Phase 4 wire"
under the bypass mechanism, not easily visible, the center lugs were from a single phase unit with the center lug tagged to the meter can.

The electrician did not notice it
The inspector did not notice it
The Gulf Power lineman did not notice it
The Gulf power lineman installed a meter and energized the transformer
EVERYone noticed it then!

The contractor was from Mobile, AL
We do not know where the meter socket was purchased
BUT examination of stock at a supply house in Pensacola turned up some units with the same defect.

It may be an isolated case of a few units. It may be a widespread problem.
As the man on "Hill Street Blues" used to say: "HEY! BE CAREFUL OUT THERE!"

Lynn

--- On Wed, 7/9/08, Lynn Adams <lhadams@co.escambia.fl.us> wrote:





_________________________
Greg Fretwell
Top
Work Gear for Electricians and the Trades

Member Spotlight
Member Since: 04/03/02
Posts: 6776
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (gfretwell), 48 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals