The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

   
Topic Options
Rate This Topic
#179256 - 07/03/08 12:47 PM using stinger to nuetral from 3ph delta
crselectric Offline
Member
Registered: 09/24/06
Posts: 134
Loc: albany, ca
I've got a 208v 2wire kiln to hookup, can I use the stinger to neutral from a 240v delta 3ph? for a 59amp 2wire plus ground hookup. I read 208v to ground from the stinger. si there a code issue? and for ocpd can I use 1 leg of a 2pole breakr or should I find a 1pole 70 amp? thanks again chris
Top
Work Gear for Electricians and the Trades
#179259 - 07/03/08 01:26 PM Re: using stinger to nuetral from 3ph delta [Re: crselectric]
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5305
Loc: Blue Collar Country
I've always been told not to do it, but I can't see a theoretical reason.

There IS a code reason ... namely, that the single pole breaker is almost certainly not listed for more than 150 v. line to neutral. Indeed, even the two pole breakers in that panel ought to be specifically listed for the use .... though I admit that they usually are not! Most two pole breakers are not listed for use with a 'stinger' either.

Another code reason is found on the panel itself. Reading the fine print on the label, again, the panel is listed only for two pole or three pole circuits with a delta service. What you're supposed to do is use this panel to feed a separate single phase panel.
Top
#179266 - 07/03/08 06:20 PM Re: using stinger to nuetral from 3ph delta [Re: renosteinke]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9066
Loc: Estero,Fl,usa
The hardware question would be, is this real 3 transformer delta? If it is Delta Vee with 2 transformers you will drag one side down (BC vs BA) and the other one up.
_________________________
Greg Fretwell
Top
#179270 - 07/03/08 07:14 PM Re: using stinger to nuetral from 3ph delta [Re: gfretwell]
crselectric Offline
Member
Registered: 09/24/06
Posts: 134
Loc: albany, ca
it must be a delta vee, there are two transformers on the pole one large and one small, pge hooked them up when we put the service in, I was only a apprentice at the time, and havent looked at the hookup to the four sets of parallel 250s we pulled in. I'll have to look up delta vee set ups, but will just tell the client to get new elements. chris
Top
#179271 - 07/03/08 07:57 PM Re: using stinger to nuetral from 3ph delta [Re: crselectric]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9066
Loc: Estero,Fl,usa
You also have to be careful with 240 single phase loads on that setup. Be sure it is using the 120/240 transformer not the stinger leg ... for the same reason. We used to run into that problem in computer rooms that were on delta services. If you can keep your single phase loads balanced around the phases you can get away with it but if they are lopsided AB/BC it can screw up the balance. (assuming orange is B)
_________________________
Greg Fretwell
Top
#179306 - 07/05/08 06:38 PM Re: using stinger to nuetral from 3ph delta [Re: gfretwell]
JBD Offline
Member
Registered: 07/12/01
Posts: 599
Loc: WI, USA
Any load connected to the stinger to neutral reduces the ability of the transformer to handle other "normal" line to neutral loads.

Theoretically it is possible, practically it is not advised.
Top
#179308 - 07/06/08 08:56 AM Re: using stinger to nuetral from 3ph delta [Re: JBD]
crselectric Offline
Member
Registered: 09/24/06
Posts: 134
Loc: albany, ca
the kiln says its 59 amps at 208, I called the mfg. tech, he said it would increase the amps on the circuit if run at 240v, but I think he was wrong wouldnt it lower them at 240v, this is SKUTT kilns and they build for both 208 and 240 and have electronic time/temp controllers, are there different electronics for 208 and 240? or wouldnt it be just rated for 250v, and its a resistive load so wouldnt it just get up to temperature faster? Sorry if this might seem basic, but my daddy brain isnt what it once was and its not always possible to get a quiet space. thanks again, chris
Top
#179309 - 07/06/08 11:00 AM Re: using stinger to nuetral from 3ph delta [Re: crselectric]
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5305
Loc: Blue Collar Country
When you change the voltage, a heating element is affected by the square of the change. That is, double the volts, get four times the heat.

The kiln maker ought to have replacement parts that are rated for 240 volts. This is the best solution; I've had to make such changes on commercial water heaters.
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Forum Styles
by Admin
Today at 02:22 PM
License exam
by TRUE POWER
Yesterday at 09:16 PM
Looking for older post
by sparkyinak
Yesterday at 12:27 AM
Members: Non-Members: Did you know?
by Admin
01/22/17 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM

Who's Online
1 registered (Admin), 89 Guests and 15 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Member Since: 08/17/06
Posts: 358

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals