The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
230 or 345 kV transmission lines?
by Vlado
09/24/16 09:33 AM
breaker meltdown
by crselectric
09/24/16 12:42 AM
Electrical mast flashing product
by ThomasWinfrey
09/22/16 12:14 AM
What estimating software do you recommend?
by sparky
09/21/16 07:20 PM
"Dry Run" Inspection goes awry
by HotLine1
09/20/16 07:39 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 17
gfretwell 9
sparky 9
sparky66wv 8
Vlado 6
Who's Online
0 registered (), 241 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#179233 - 07/02/08 09:26 AM 2 phase services
junkcollector Offline
Member

Registered: 04/15/07
Posts: 35
Loc: Central MN
This topic has probably been brought up here before, but through some searching I found nothing. (Sorry if I'm beating a dead horse )

My question is, has anyone worked in a building that had 2 phase power? Was it POCO supplied, if so, could you explain the transformer hookup? (If overhead) What kind of disconnects / panelboards where used? I seen a few pictures of a smaller 2 phase service on a home inspector site. I consisted of 2 FPE panelboards, both feed with 2 hots and shared a nuetral. The meter said 2 phase, 5 wire. It had 5 wires for a utility drop. (Pics didn't show transformer hookup)

Just wondering if anyone had any information or examples on what a service consisted of. I know this is pretty much an obsolete system, but may well still exist in larger cities so it would be interesting to know how modern components, panelboards, etc are connected. I have seen diagrams and schematics for a Scott-T connection, and the theoretical aspects of changing 3 phase to 2 phase make sense, I was more or less wondering about the physical aspects.

Thanks everyone for any tidbits you can provide. \:\)

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#179242 - 07/02/08 06:30 PM Re: 2 phase services [Re: junkcollector]
JBD Offline
Member

Registered: 07/12/01
Posts: 599
Loc: WI, USA
I have seen diagrams in literature from Cooper Power Systems and in Ugly's book.

The common conductor needs to be sized very carefully. On a standard 2-phase 3-wire circuit the common conductor needs to be 1.414x the line conductors.

Top
#179255 - 07/03/08 12:18 PM Re: 2 phase services [Re: JBD]
RODALCO Offline
Member

Registered: 12/08/05
Posts: 862
Loc: Titirangi, Akld, New Zealand
The meter 2 phase 5 wire has the following terminals.

Phase 1 line
Phase 1 load
Phase 2 line
Phase 2 load
Neutral

so 5 wires are used.
_________________________
The product of rotation, excitation and flux produces electricty.

Top
#179305 - 07/05/08 06:27 PM Re: 2 phase services [Re: RODALCO]
JBD Offline
Member

Registered: 07/12/01
Posts: 599
Loc: WI, USA
 Originally Posted By: RODALCO
The meter 2 phase 5 wire has the following terminals.

Phase 1 line
Phase 1 load
Phase 2 line
Phase 2 load
Neutral

so 5 wires are used.


A 2-phase 5-wire system is basically (2) 3-wire systems, loads were never connected between Phase 1 and Phase 2.