The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
10/24/16 08:46 PM
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 7
ghost307 7
renosteinke 6
Potseal 4
Who's Online
0 registered (), 339 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#179106 - 06/26/08 04:22 AM Water bond size
wire_twister Offline

Registered: 07/25/07
Posts: 265
Loc: Georgia USA
I just finished the slab work on a metal building. Building will have a 600a service, 600a distribution panel, and several smaller panels through out. Now the question, the drawing specified a 3/0 copper wire to bond the plumbing, is this the norm or is it a little large for its use? Just wondering.

Life is tough, Life is tougher when you are stupid

Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#179108 - 06/26/08 06:59 AM Re: Water bond size [Re: wire_twister]
Zapped Offline

Registered: 10/01/02
Posts: 481
Loc: Huntington Beach, CA, USA
I don't see any reason to deviate from the drawing twister, unless the drawing violates code. If the engineer has determined that 3/0 copper is required to clear the worst-case short, then I would not argue with him. Deviating from the engineer's specs can only lead to trouble for you.

Good Luck!

#179109 - 06/26/08 08:33 AM Re: Water bond size [Re: Zapped]
Alan Nadon Offline

Registered: 03/10/05
Posts: 398
Loc: Elkhart, IN. USA
Seems a little larger than normal. What size service entrance conductors ? Section 250.66 would list the required GEC. What the Eng. specified is what you need to build, unless he allows a change order.
What is built can always exceed Code.
If it was easy, anyone could do it.

#179110 - 06/26/08 08:51 AM Re: Water bond size [Re: Alan Nadon]
SteveFehr Offline

Registered: 03/19/05
Posts: 1192
Loc: Chesapeake, VA
What service conductors did he spec out? 3/0 is the right size for 1500kcmil USE (625A ampacity) or similar. If multiple smaller cables are used, 2/0 may be acceptable, but you'd end up having to derate for # of conductors in a raceway, which would put you right back at 3/0. Seems like a reasonable requirement to me.

You could always call the engineer and ask.

#179111 - 06/26/08 10:26 AM Re: Water bond size [Re: SteveFehr]
renosteinke Offline
Cat Servant

Registered: 01/22/05
Posts: 5305
Loc: Blue Collar Country
It's a situation like this that highlights some of the confusion the code has in it, especially in Article 250.

After all, just what are we attempting to accomplish with that wire? The ground rod / ufer / whatever only requires a #6, regardless of the service size.

Clearing faults? Is there ANY possible circumstance where the plumbing could possibly be exposed to the full service fault current? Does it ever make sense to require more copper in the wire than there is in the pipe itself?

I think we're wrestling a dinosaur here .... the water line once was the grounding electrode, yet today we're -at most - using it as a supplementary electrode. More realistically, we are bonding the pipe, to protect against it being accidentally energized.

Still, no harm done .... and until the code panels get their acts together (maybe even get an grammar expert involved), engineers will be stuck specifying idiocy.

#179114 - 06/26/08 12:57 PM Re: Water bond size [Re: renosteinke]
gfretwell Offline


Registered: 07/20/04
Posts: 9026
Loc: Estero,Fl,usa
I agree with John, the 250.66 requirement for connection to water pipe is a remnant of the days when water supply lines were metal and that was your best ground electrode. Now days the plumbing lateral into a building will generally be PVC and the only real grounding will happen with the inadvertent connection to building steel via the pipe supports.
Greg Fretwell

#179135 - 06/27/08 02:57 PM Re: Water bond size [Re: gfretwell]
luckyshadow Offline

Registered: 01/04/05
Posts: 305
Loc: Maryland USA
Yes it does seem to be large.
But keep in mind the nEC is a minimum


ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals