The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
10/24/16 08:46 PM
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 7
ghost307 7
renosteinke 6
Potseal 4
Who's Online
0 registered (), 280 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#179040 - 06/23/08 08:09 AM Need help with service calculation ???
site351 Offline

Registered: 06/10/07
Posts: 19
Loc: Tennessee

Got a question and don't have a code book....

A 3" P.V.C.conduit is ran from under ground transformers
to electric meter packs with 150 breakers. All meter packs
are main lug, no main breaker. Some meter packs contain six
meters and some five, some four. 120/240 volt residential.
I know I can parallel the Pratt 250-250-4/0 alu. in a 3"
p.v.c. that big enough to handle the load for
the five and six meter packs ?
6x 150= 900 total amps for the six banger @ 45% = 405
amps ? can't remember how much to derate...
Five meter pack may work with 250...just not sure about the six ... thanks....

2014 / 2011 NEC & Related Books and Study Guides
#179041 - 06/23/08 09:14 AM Re: Need help with service calculation ??? [Re: site351]
sabrown Offline

Registered: 12/12/02
Posts: 297
Loc: Ogden, Utah, USA
Assuming that you have done calculations on the services and have found that they all are at 150 amps. 5 residential services can be calculated at .45 for a total of 337.5 amps (see 220.84).

6 residential services can be calculated at .44 for a total of 396 amps. Same code reference. Parallel conductor installation of 250 kcmil are good for the 400 amp total (255x2x.8 NEC 310.15(B)(2)(a)) if allowed by your AHJ.

I did not check the nuetral. This also makes the assumption that you meet the multi-residential requirements.