The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Forum Software Upgrade coming soon...
by Webmaster
Today at 12:03 AM
Re: Fabricating Guards out of Lexan?
by frank
Yesterday at 04:11 PM
Would ELV branch circuits be a good idea?
by gfretwell
Yesterday at 01:26 PM
Why cables look like they do
by Texas_Ranger
Yesterday at 12:33 PM
100% breakers?
by Texas_Ranger
01/16/17 06:13 AM
New in the Gallery:
Desk-mounted "power-board"
Top Posters (30 Days)
Webmaster 20
HotLine1 19
gfretwell 13
Trumpy 12
ghost307 12
Who's Online
0 registered (), 0 Guests and 63 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#179040 - 06/23/08 08:09 AM Need help with service calculation ???
site351 Offline
Member

Registered: 06/10/07
Posts: 19
Loc: Tennessee

Got a question and don't have a code book....

A 3" P.V.C.conduit is ran from under ground transformers
to electric meter packs with 150 breakers. All meter packs
are main lug, no main breaker. Some meter packs contain six
meters and some five, some four. 120/240 volt residential.
I know I can parallel the Pratt 250-250-4/0 alu. in a 3"
p.v.c. pipe...is that big enough to handle the load for
the five and six meter packs ?
6x 150= 900 total amps for the six banger @ 45% = 405
amps ? can't remember how much to derate...
Five meter pack may work with 250...just not sure about the six ... thanks....

Top
2017 / 2014 NEC & Related Books and Study Guides
#179041 - 06/23/08 09:14 AM Re: Need help with service calculation ??? [Re: site351]
sabrown Offline
Member

Registered: 12/12/02
Posts: 298
Loc: Ogden, Utah, USA
Assuming that you have done calculations on the services and have found that they all are at 150 amps. 5 residential services can be calculated at .45 for a total of 337.5 amps (see 220.84).

6 residential services can be calculated at .44 for a total of 396 amps. Same code reference. Parallel conductor installation of 250 kcmil are good for the 400 amp total (255x2x.8 NEC 310.15(B)(2)(a)) if allowed by your AHJ.

I did not check the nuetral. This also makes the assumption that you meet the multi-residential requirements.

Top