#178768 - 06/11/08 10:36 AM Outdoor hot tubs
Oh Well Offline
Member
Registered: 12/12/05
Posts: 12
Hello With regards to spas and hot tubs I'm told that rule 68-404 requires that a means of disconnect in case of emergencies must be located within sight of the tub. Could this possibly be a push button controlling a contactor inside the house? Or would simply using the button to trip the GFI be acceptable? Thanks in advance. Oh Well
Top
Tools for Electricians:
#178769 - 06/11/08 10:46 AM Re: Outdoor hot tubs [Re: Oh Well]
mr_electrician Offline
Member
Registered: 06/22/07
Posts: 106
Loc: London, Ontario
Originally Posted By Oh Well
Hello With regards to spas and hot tubs I'm told that rule 68-404 requires that a means of disconnect in case of emergencies must be located within sight of the tub. Could this possibly be a push button controlling a contactor inside the house? Or would simply using the button to trip the GFI be acceptable? Thanks in advance. Oh Well


68-404 is talking about a hut tub control box. Usually the hot tub will come with one and located behind a removable cover. If not then the control box can be no closer that 1 meter horozontaly to the hot tub. This is so no one in the hot tub can contact any electrical equipment while sitting in it.


Edited by mr_electrician (06/11/08 10:48 AM)
_________________________
Never trust an electrician with no eyebrows!!
Top
#178798 - 06/12/08 08:54 AM Re: Outdoor hot tubs [Re: mr_electrician]
mikesh Offline
Member
Registered: 06/07/06
Posts: 613
Loc: Victoria, BC, Canada
If you are referring to 68-404 (4) A new to the 2006 CEC rule. Then a push-button with a contactor may be acceptable to your inspection department but check first as some jurisdictions won't accept a magnetic contactor as a disconnect. The control button should lock once pressed to ensure the contactor if acceptable won't reclose after you take your hand off the button.
This is for hot tubs and spas located in public locations like a community pool, hotel, or apartment building. You don't have to install this disconnect in a Single family dwelling except perhaps if a bed and breakfast is operating there. The rule came from a couple of entrapment drownings where part of a person or their clothing was trapped in the water inlet and the occupant drowned.
Top

Member Spotlight
Member Since: 12/24/00
Posts: 4259
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 87 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals