#178705 - 06/09/08 07:17 PM 5% rule.
Sandro Offline
Member
Registered: 12/30/01
Posts: 444
Loc: Stoney Creek, ON, Canada
300 mcm T90Nylon is rated for 295amps. Using the 5% rule, one could use parallel 300mcm runs for a 600 amp service?
Top
Tools for Electricians:
#178706 - 06/09/08 08:22 PM Re: 5% rule. [Re: Sandro]
twh Offline
Member
Registered: 03/11/04
Posts: 901
Loc: Regina, Sask.
If your calculated demand is 620 amps, you can put in a 590 amp service, which would be fused at 600 amps according to 14-104, if a 590 amp fuse is not available. That is, you can install a 590 amp service and fuse it at 600 amps.
Top
#178920 - 06/15/08 07:32 PM Re: 5% rule. [Re: twh]
ThorahSparky Offline
Junior Member
Registered: 04/13/03
Posts: 13
Loc: Orillia,ON,Canada
Generally if you are considering applying the 5% rule I would first run it by your local inspector. Yes, it is a rule but doing so makes for a better relationship, especially if you don't know him/her.
Top

Member Spotlight
Member Since: 12/24/00
Posts: 4259
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 54 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals